Selecting Baud Rate for PCOM


dbolg

Recommended Posts

Hello,

 

I have a .net application that connects to a 570 via RS-232 using System.IO.Ports.SerialPort. Normally, it will connect. However, when playing with different baud rates, it sometimes does not connect until I connect the same PC with any Unitronics software (Visilogic or Remote Operator). My question is this:

 

With VIsilogic, it appears that you can define the baud rate to anything in the connection properties and it always connects. How does the controller adapt accordingly? I think "out of the box", the rate is set to 115200.

 

If I change my application to 57600, it failes to connect. But, if I connect using Visilogic @ 57600 it works. I go back to my application and then it works. I am trying to determine what Visilogic is doing that I am not. My connection looks like this:

 

                    // Connect to the PLC
                    try
                    {
                        string comPort = Properties.Settings.Default.CommPort;
                        int comBdRate = Properties.Settings.Default.CommBdRate;
                        int comTimeOut = Properties.Settings.Default.CommTimeOut;
                        _serialPort.PortName = comPort;
                        _serialPort.BaudRate = comBdRate;
                        _serialPort.DataBits = 8;
                        _serialPort.Parity = Parity.None;
                        _serialPort.Handshake = Handshake.None;
                        _serialPort.ReadTimeout = comTimeOut;
                        _serialPort.NewLine = "\r";
                        _serialPort.Open();
                    }
                    catch (Exception)
                    {
                        // Disconnect from the PLC
                        _serialPort.Close();
                    }
 
Once this executes, I begin sending PCOM commands:
 
            try
            {
                // Send the message out the serial port.
                _serialPort.DiscardInBuffer();
                _serialPort.WriteLine(message);
                // Verify the message was received, catch the timeout
                string response = _serialPort.ReadTo("/A00SBF5");
                if (response == "/A00SBF5")
                {
                    //do nothing, success!!
                }
            }
            catch (Exception)
            {
                _connectionLost = true;
                _serialPort.Close();
                return -1;
            }
 
The _serialPort.ReadTo() catches the timeout (default 1 sec). When that occurs, we assume we lost the connection. Is there something I should be doing to prime the port first?
 
Thanks!
 
 
 
 
 
Link to comment
Share on other sites

You cannot communicate with the PLC if the baudrates does not match, so the only way that is left is using hardware signals.

If you set the BreakState of the serial port, then it signals the PLC to switch to 9600.

            serial.BreakState = true;
            Thread.Sleep(500);
            serial.BreakState = false;
            Thread.Sleep(1000);


Now you need to tell the PLC that you want to change the baud rate. The command would be:
        internal string BreakCommand()
        {
            string breakCommand = "CPC";
            breakCommand += "1"; // plc port
            breakCommand += "T"; // Temp change
            switch (BaudRate)
            {
                case BaudRate.BR110:
                    breakCommand += "01";
                    break;
                case BaudRate.BR300:
                    breakCommand += "02";
                    break;
                case BaudRate.BR600:
                    breakCommand += "03";
                    break;
                case BaudRate.BR1200:
                    breakCommand += "04";
                    break;
                case BaudRate.BR2400:
                    breakCommand += "05";
                    break;
                case BaudRate.BR4800:
                    breakCommand += "06";
                    break;
                case BaudRate.BR9600:
                    breakCommand += "07";
                    break;
                case BaudRate.BR19200:
                    breakCommand += "08";
                    break;
                case BaudRate.BR38400:
                    breakCommand += "09";
                    break;
                case BaudRate.BR57600:
                    breakCommand += "0A";
                    break;
                case BaudRate.BR115200:
                    breakCommand += "0B";
                    break;
            }

            breakCommand += "FF"; // Timeout - no change
            breakCommand += "FF"; // Flow Control - no change
            return breakCommand;
        }


For the result you got, you add the STX + Unit ID + Checksum + ETX like in any ASCII command:
STX + Unit ID + Command + Checksum + ETX


As I said, you need to change your baud rate to 9600 in order to send that command.
For that, you need to disconnect the serial port (since changing the baud rate while the connection is opened will result an exception).

            serial.Disconnect();
            serial.BaudRate = BaudRate.BR9600;
            serial.Connect();
            Thread.Sleep(1000);
            serial.WriteLine(_theResultCommandThatYouGot);
            serial.Disconnect();
            serial.BaudRate = originalBaudRate; // This is the baud rate that you told the PLC you want to use
            serial.Connect();

// now you are good to go.
  • Like 1
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...