darknesspic Posted July 1, 2015 Report Share Posted July 1, 2015 Dear All I'm using V280 with RS232 send with condition 1time per 1press the button (check the rising edge)but the result send the data all the time. Thank you V280-XX01-A00Rev02.vlp Quote Link to comment Share on other sites More sharing options...
s.pratt Posted July 1, 2015 Report Share Posted July 1, 2015 Hello, After running your program here on a V280, we received the same results. The problem is running the Protocol Config and COM Init in a subroutine off of SB2. Please move the Protocol Config and COM Init to the Main Routine off of SB2 and see if the message sends correctly. Quote Link to comment Share on other sites More sharing options...
darknesspic Posted July 2, 2015 Author Report Share Posted July 2, 2015 Thanks for your advice l got the solution Quote Link to comment Share on other sites More sharing options...