    Hello, It seems that indeed the BinLib version cause to this issue. Please try to recover the PLC as follow: Use COM1 RS232 115200 baud rate 2sec time out Connect 6 wire cable instead of the 4 wire cable. Reboot the PLC The PLC should beep > tap once to stop the beeping Go to VisiLogic>communication & O/S, the 4th tab is system modes Check the communication by clicking on the GET button If you have a communication>Switch to Factory BOOT Go to O/S tab>check Download only the BinLib by clicking on the Advance button>BinLib (only) If the download will success, then replace to 4 wire back and download the BOOT and then the O/S.
×
×