Hi. We have temp / hum sensor, valve controller and damper controller with unitronics vfd connected to unistream plc. We have trouble with network if we read and write to the valve and vfd. If we only write it seems to be working but as soon as we read a value the we loose connection or control of the vfd. The modbus 485 comm port is added to the plc. It caanot be set up as vfd port then the other modbus units does not work. So the port is setup as modbus panel. All setting correct as we can write the freq of the drive as needed. It's only if you want to read as well write that problem start. Any ideas please.
-
Scada comms problem
RBC replied to RBC's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi. Thanks for answer. Scada is master. If scada comms lost plc and drives still have comms be it with short intermittent loss of comms. second or so. The program is on laptop in west africa. Client try to sort it out as we can't travel there to assist. -
Hi. We installed 3 x V570 plc's running on ethernet network. Also connected Indusoft scada system to system. Delta vsd run also on same network. All working fine and then sometimes comms to scada stops. Also comms to VSD's not constant. If comms to scada laptop fails we have to restart plc's to get comms again. Any suggestions or help will be appreciated
-
-
Error, Command: 0x81, Status: 0x25 [ID: 1028] MOTCP Read Block - Station: 192.168.7.120:502:255, Address: 0X:1 to 0X:296 > Status: 37 [ID: 1028] Tx:00 00 00 00 00 06 FF 03 00 00 00 40 [ID: 1028] Rx:00 00 00 00 00 83 FF 83 80 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 ...Rx:00 BB A0 00 0D 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 ...Rx:00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 ...Rx:00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 ...Rx:00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 ...Rx:00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 Error, Command: 0x83, Status: 0x80 [ID: 1028] MOTCP Read Block - Station: 192.168.7.120:502:255, Address: 4X:1 to 4X:64 > Status: 128 [ID: 1028] Tx:00 00 00 00 00 06 FF 03 00 40 00 0C [ID: 1028] Rx:00 00 00 00 00 1B FF 03 18 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 ...Rx:00 BB A0 00 0D 00 00 00 00 [ID: 1028] MOTCP Read Block - Station: 192.168.7.120:502:255, Address: 4X:65 to 4X:76 > Ok If I change block size to 64 then this happens.
-
Error, Command: 0x81, Status: 0x25 [ID: 1168] MOTCP Read Block - Station: 192.168.7.120:502:255, Address: 0X:1 to 0X:296 > Status: 37 Changed all the 1x to 0x and get this error.
-
Error, Command: 0x82, Status: 0x1C [ID: 12B4] MOTCP Read Block - Station: 192.168.7.120:502:255, Address: 1X:1 to 1X:222 > Status: 28 Statur :28 of the last line. Will modify today again and see what happens. When I tried 0x for the inputs and outputs it gives me different error messages again. Also the registers on the 3x was on 4x but did not want to work. The 2nd pic I attach is the settings of driver. If I make the 32 block size 64 as in other systems I loose the values as well. Is there something on the Unitronics side that I need to change? Thanks. If you can assist with teamviewer then maybe it can help. What other scada system do you use now instead of Indusoft. We build drying room for fresh fruits and use basically for temp logging and machine status with the scada. Thanks again for all assistance. Sitting in West Africa now with the installation so internet and things not that reliable. Rodger
-
Hi Joe. Thanks for the reply. We have 1x setup in other systems for inputs, outputs and internal coils and it worked. I've changed the internal coils to 0x now and they work. But my inputs and outputs than is on 1x does not work. [ID: 2524] MOTCP Read Block - Station: 192.168.7.120:502:255, Address: 0X:252 to 0X:296 > Ok [ID: 2524] Tx:00 00 00 00 00 06 FF 02 00 00 00 DE [ID: 2524] Rx:00 00 00 00 00 1F FF 82 1C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 ...Rx:00 00 00 00 00 00 00 00 00 00 00 00 00 Error, Command: 0x82, Status: 0x1C [ID: 2524] MOTCP Read Block - Station: 192.168.7.120:502:255, Address: 1X:1 to 1X:222 > Status: 28 [ID: 2524] Tx:00 00 00 00 00 06 FF 04 00 00 00 16 [ID: 2524] Rx:00 00 00 00 00 2F FF 04 2C 00 25 00 25 00 26 00 24 00 24 00 26 00 24 00 ...Rx:26 00 44 00 1E 00 1E FF FF FF FF 00 00 00 00 00 00 00 00 00 00 00 00 00 ...Rx:00 00 00 00 00 [ID: 2524] MOTCP Read Block - Station: 192.168.7.120:502:255, Address: 3X:1 to 3X:22 > Ok Do you know what the status 28 is in that row. Thanks.
-
Hi. W've done couple of projects linking unilogics and unistream plc to indusoft scada system. Now I'm battling to get comms to the io part of the plc. Registervalue's we can get but any bolean point no comms. Anybody have experience between indusoft and unistream plc. Thanks.
-
Hi. Hope someone can help. I've got 2 analog input cards in my system. All configured the same. The one card my temp is stable but the 2nd card the reading fluctuates a lot. from 1 to 35 to 17 and so on. Connected pt100 connected to convertor to 4-20ma directly in panel to see is cable fault. Still the same. Any ideas please. Thanks.
-
Hi. Have 3 PID's with the same settings but 1 is not working the same. Valve closes too soon and never reach setpoint. Same settings and 32 parameters the same
-
Hi. My client have different sequences with tanks and pumps and pack stations. I need to provide selection screen from which he wants to select the sequence he wants to use. Its to many different options to develope screens for the selections. Is there a way to greate drop down selection list wich will enable a MB according the seletion made. Any suggestion will be apreciated. Thanks Rodger
-
V570 comms with slc500 on rs232 port
RBC replied to RBC's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi. Ive looked at it but dont understand. Im new to allen bradley software. 2 things. Do you have example of unitronics and allen bradley programs showing how to send and receive data. Lets say in the V570 i'm using mb100-200 and it must be put into b11 on plc503 to switch outputs and wants to use b10 to get info back from plc503. -
Hi. Will it work on V570 as well? Thanks.
-
Hi. how do you reset accumalating timer.
-
Ethernet network
RBC replied to RBC's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Thanks. Thats what i had in mind but not sure how to do. Will sit and figure it out tonight so i can implement it tommorrow.