if you try to SSH to the PLC ip you will receive login prompt ...
if this system runs linux this can help to menage C or Python scripting and brings lot of abilities for advanced user and application
i found the issue !!!
google permit sending 100 email per day and close the SMTP access for 24 hours when pass this restriction
if the logic to send email is drive by "Direct Contact" and not "Positive Transition Coil" the logic will send email every PLC loop and block the account immediately ...
i think the sending email need to improve with function that will limit sending quotas to prevent the PLC to block the account when logic problem is accrued
the file on the predefined folder in 0:/AlarmLog/AlarmLogs/ change the name on any event
i try to put from example - the file name #"AlarmLog08_04_19-21_02_54.zip" and it works but the application require to send the latest event log when critical event was trigger
the problem is that the file name is change every day so i can't send the latest alarm log like i have on the pre defined folder 0:/AlarmLog/
there is missing description if the file name need to include the file name extension after the dot
when sending screen shoot it require to add .jpg to the file name and when sending DT it not require ?
appreciate your support
i using the Gmail SMTP and receive Error -1
i using correct DNS 8.8.8.8 and i ping it from unistream PLC ,i using correct gateway
i use smtp.gmail.com:465 server
i also enabled gmail third party connection and check it with my out look
can it be that this service was changed or google block it ?
Correct , as you can see on the picture i put marker on the chart and it present correct value 1 ,while Y axis present value somewhere in between 0 to 1 .
it will be useful in the future if the user can better customize the trend and the division line properties for example color thickness number of separation line )
also to present process in one file for more then 24 hours (year months)
Thank you for support
i install the latest version 1.25.54 and i have same issue
you can simply restore it by crate Data Sampler of integer value ,and display it on trend with #0 to #6 value .
when start sampling you will see that Y axis have unit problem with the integer value .
the trends using real and int numbers
the problem is with INTEGER NUMBER the Y axis is not relevant to the correct value
i use the latest UniLogic 1.24.56
this is Display bug !
if you see on the picture the Value that i point when X = 17:43:31 Y = 1 it display the correct value on the pointing ,but axis Y on the chart holds incorrect value
you can also see that the separation line ticks holds the value 0,1,3,4,6 this division is INCORRECT display ,it should be 0,2,4,6 or 0,1,2,3,4,5 .
Hello,
I want to change the number of digits that display after the prescription point on real value displayed on data table all the real values prescription points displayed with 6 digit and take lot of area in the Data table
i want to see the correct Y axis value on the PLC chart
exporting to excel is not present the immediately value display
also negative value present as positive on the Y axis .
can it be that value on graph is correct when placing the pointing on the carve
but the Y axis shows incorrect value ?
on the image the white line value is "1" and the Y axis shows something between 0 to 1
I HAVE SAME ISSUE
Can't attached AlarmLog when try to do so i recive -4 error
what is the filename that i need to put to send the latest Alarm Log
i success to send DT file and email without attachments
can you send sample on how to send the AlarmLog on EMAIL ?