Posts posted by Mahde
-
-
please look at the attached picture..
the command should transfer or i have to add any control char?in hyper-terminal from pc no more char needed..
only writing 1go5 and the valve start moving
-
Hi
I have a multi-valve that can communicate with rs232 by hyper terminal in normal pc.
Iam trying to connect the valve by v570 visio plcs.
I understand from the unitronics examples that i can use send protocol
One comand i can send is : 1go5
This command for example move the valve to port 5.
In hyper terminal after i connect i simply type 1go5 and the valve start moving.
What i shoud write in send protocol FB?
I have to translate the 1go5 to ASCI code before?
Can anybody direct me for this?
Thank you
RS232 Serial connection + command to multi-valve
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
it's Work!!
Thank you very much Joe T.