  1. To restart and idle EX-RC1 do the following ( with only a 24v DC PSU connected to it ): - With the power off switch all the DIP switches On ( Boot Strap Mode ) - Power it, it will power up with steady PWR LED and flashing I/O COMM and Bus COMM - You can now connect via Prg port 57600 BAUD, Get OPLC information returns Model EX-RC1-BOOT, Hardware A, OS Version 2.00 (20) or similar - Power it off, change DIP switch all OFF ( Stop Mode ) - Power it, it will power up with steady PWR and flashing I/O COMM - Get OPLC Information returns Model EX-RC1, Hardware A and OS Version 5.04 (14) or similar - Get PLC Status will show Run/Stop = Stop - Press the Run button, Get PLC Status will show Run/Stop = Run - Power it off, change DIP switches to required address 1 to 60 - Power it, it will power up with steady PWR and flashing Bus COMM Normal function is restored. Best regards Christoph
×
×