cable for modbus communication on M91

Recommended Posts

All our controllers use Modbus RTU on their serial ports. In addition, almost all Vision models (except V120) support Modbus IP, if optional Ethernet card was installed.

Share this post


Link to post
Share on other sites

Thanks Emil,

i'v loaded the Modbus slave demo program from the U90 ladder examples.

and try to read data with Modbus Poll application,

now ipost-9027-0-49614000-1346573123_thumb.jpg'm getting a time out message,

does somone have any idea whats wrong ,

attach is a screenshot from Modbus poll .

Share this post


Link to post
Share on other sites

First of all - disable Flow control.

Check if the controller is set to ID1. The standard example is set ot ID2.

Please check again the communication cable.

I hope these tips will help.