It is the second time I have the same problem with AO6X analog output modules - although in the Hardware Configuration I choose 4-20mA option for the current outputs, they produce 0-20mA anyway! Norlmally I use it with an inverters set to 4-20mA frequncy reference. OK, I switched inverters to 0-20mA, but there's another issue - 20mA does not correspond with the value of 4095 in an assigned MI, but with 4080! Very odd behaviour, not a real problem to me becuse I made it work anyway, but I had to report it here.

My best regards to all!

post-281-0-54195200-1370526502_thumb.jpg

post-281-0-15253300-1370526517_thumb.jpg

post-281-0-76657800-1370526531_thumb.jpg

Share this post


Link to post
Share on other sites

Dear Nacho,

thanks a lot for the remark you've made, somehow I missed it while reading the Guide. :huh:

On the other hand, this means that the unit actually produces 0-20mA in both modes, so one has to use linearization network (or some similar calculation method) to scale 0-OUTmax in 819-4095 units instead of 0-4095. Logical question is then why there is a switch in a Hardware Configuration menu, i.e. what really changes when I change it? It seems - nothing.

Also, I don't expect output current to be dependent of the inverter input impedance as long as it is within specified range.

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...