Ladder Linearize help information
I am trying to use the linearize block in the ladder program.
When I search the help file I can not find the information for this block.  There are six registers (tags) required.
A, B, C, D, E, F
F is the result or the scaled value.
Is A input value?
B and C the Raw values for min and max?
Is D and E the engineering units?
I know my raw value is from 2007 to 34835.  The Scaled value is from 0 to 138.0 Feet.
So Does A = The value from Pressure transmitter (Not connected to an Analog input.  Getting through communications connection)
B = 2007
C = 34835
D = 0
E = 1380
F = Result?
Hi Michael,
First of all note that if you will mouse over the parameters (A, B, C, D etc..) you will get a tooltip with the description of the specific parameter.
A - input value
B - X1  2007
C - Y1  0
D - X2 34835
E - Y2  1380
F - Result