protechnologia Posted June 9, 2014 Report Share Posted June 9, 2014 I have a signle PLC over Ethernet configured in UniOPC. Why if I set Update Rate to value higher than 3 sec, (00:00:03:00) after couple of seconds values in UniOPC freezes and stop changing? Quote Link to comment Share on other sites More sharing options...
protechnologia Posted June 11, 2014 Author Report Share Posted June 11, 2014 I probably found my answer. It was due to SI103-106 operands. I had them set to 50 causing to disconnect after 5 secs. Quote Link to comment Share on other sites More sharing options...