Gents,

I have an application developed in a V570. I have basic Modbus TCP comms up and running. I am able to remotely monitor and control all 'MI' points in my program but I am having trouble getting any 'MB's to work at all. I have used the help doc to calculate the external MB offset. (Can be found at: Communications\Communication FBs\Modbus IP\Read Imputs then click the link to 'Slave Address Tables')

This should be simple as the offset is quite simply 30001 + MB Addr. For example I am trying to monitor MB3107 wich maps to 33108 as an external MB addr. However this entire range is dead when monitoring from my Modbus OPC server. At least this is the way I understand it from the doc.

I am also having the same problem with reading O and I directly.

Any help would be much appreciated.

Link to comment
Share on other sites

Hi,

Please note that there are 2 slave address tables, one for standard vision and one for enhanced vision.

You need to use the Enhanced slave address table - please note that the addresses are in HEX.

For reading coils i assume that the address will be 10001 + offset - Can you try it?

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...