Currently I'm using the MODBUS RTU to DMX converter from t-mac in the UK. But some DMX drivers cannot get the correct data from the converter. 

Is there another way to control a DMX driver with a V350? This may be done with an interface (CANBUS/MODBUS IP to DMX) or directly from the PLC. 

 

Thanks in advance,

 

Greets Edwin

 

Share this post


Link to post
Share on other sites

Hi Edwin,

Unfortunately it is not possible to communicate with DMX 512 devices using our Vision controllers.

The DMX 512 protocol communications baud rate is 250 Kbaud, which is not supported by Unitronics PLC's. 

Share this post