Working today with a V1040, I found something I was not aware of; complex HMI screens use a tremendous amount of scan time.  I have placed 100 very small bar graphs on the screen with 100 very small bianary objects to create a graphic display of a process control profile.  Whenever this screen is active the scan time will increase from 2 ms to 10 ms and this is not good for my application.  I am trying to control a rather fast process with 100 profile points via analog output and 10ms is on the edge of non-functionality.  Is there a way to slow the refresh rate on this particular HMI screen, so as to decrease the scan time?
Another suggestion mentioned in a related topic was to use one PLC dedicated to the processing, with some form of communication to a second PLC that handles the display.  Don't transfer as much information (if the display itself isn't critical).
Or as Flex727 mentioned, look into UniStream.