I am using a IO-D16A3-RO16 and have 3 flow sensors I need to attach, I have two attached to the HSC and want to know if possible and how to do it, is connect the other flow sensor up to a standard digital input?

The flow sensor can give a max pulse rate of 73.33 pulses per second.

Share this post


Link to post
Share on other sites

Hello,

 

The response time of the normal digital inputs are 10ms.  Therefore, we do not suggest attaching a device that has a frequency of 50Hz and above.  Anything over 50Hz, you will run the risk of missing pulses.

 