Hello,

 

I am new in this forum and in unitronics, for this reason I have too many problems when I set up V700.

 

  1. I am following the manual "Using Ethernet" to V700 and I could not watch the IP address with I need to set up downloads throught the ethernet cable PC-PLC.
  2. When I try to simulate in visilogic anyprogram appears the next window "Run-time error 5 invalid procedure call or argument"

I will start this topic with these questions. Thanks.

 

Link to comment
Share on other sites

We recommend running our software as an administrator. This is a Windows setting that if not applied can generate the run time errors as you have seen. It is not likely anything you have done or set up within your project.

 

To run VisiLogic as an administrator, right click on the VisiLogic Icon, choose Properties, navigate to the Compatibility tag, and select the box labeled ‘Run this program as an administrator’. Hopefully this should eliminate the error you are experiencing.

 

How did you set the IP address within the controller? Did you program it over serial first, or did you set the IP address through info mode in the controller?

Link to comment
Share on other sites

There was not any information in your reply.

 

Were you successful in solving the issue?

Sorry, I lost the internet connection and the reply appears in white.

 

Yes, the errors were gone :)

 

Okey, I set up the unitronics' program for v700 in order to configurate ethernet connection:

fdd46231ab3f17f940eb6e116b7f6bd9o.jpg

 

My purpouse is set up the IP address to connect the V700 directly to the ethernet port to speed up the transmition. But I dont know how to get this IP

fe7ad6e9b86544ca963f5fb10fb0dc23o.jpg

 

Thanks

Link to comment
Share on other sites

Yes, as Joe mentioned you must first initialize the Ethernet card using a specific function block (TCP/IP Card Init). This function block can be found under the COM TCP/IP menu in VisiLogic. The IP Address, Subnet Mask, and Default Gateway will be defined in this block either using a defined value, or by linking a vector of 4 MI's for each address.

Link to comment
Share on other sites

So the conclusion is, if I want a dynamic IP address linked to anyvalue I will use vectors with 4 MIs and if I want a static address I can define directly to xxx.xxx.xxx.xxx in each field.

 

So, once I set up IP/TCP protocol, could I introduce this address in the communication port to download projects PC-PLC faster than USB?

Link to comment
Share on other sites

  • MVP 2023

Yes you can do that. Socket 1 will default to Port 20256 for PLC-PC communications. If you initialize Socket 1 to a different port, then you will need to initialize one of the other sockets to port 20256. Be sure you also use the PLC Name function block to give the PLC a useful name for communications from your PC.

Link to comment
Share on other sites

I have another question, sorry because I am newbie with Unitronics's PLC. A vector is a composed of different operands, for example, I set up one in MI0 with lenght 4, the full vector is MI0,MI1,MI2,MI3, the question is if I have to set up IP addresss for example 198.168.1.1 each value corresponds to each MI which will be the "Vector address"?

 

I only can link one MI to the IP addrees is it MI0? then visilogic knows that MI1,MI2,MI3 are linked to this one?

Link to comment
Share on other sites

  • 2 weeks later...

I try to set up the ethernet card again and the error SB168 comes up, then I power up SB168 and visilogic show me an error of compatibility with V700.

Anybody have idea about this?

 

What I am trying to do is connect PC-PLC, I was reading about MODBUS, I don't know if I need to set up MODBUS settings.

 

Thanks

Link to comment
Share on other sites

  • MVP 2023

Be sure your PC and PLC are set up on the same subnet (e.g. 192.168.1.xxx). Check in INFO Mode what the IP address of the PLC is and the PLC Name and be sure those are properly entered in the communications section of VisiLogic. Make sure you are connecting the PLC and PC either through a hub or with a crossover cable.

Link to comment
Share on other sites

  • MVP 2023

I don't know if you really need the PLC to be the Master, by try it the other way first. Initialize the PLC Socket to Port 20256 and Slave. Set up the PC communications in VisiLogic to TCP/IP (Call). Confirm the PLC Name and IP address are correct, then try to initiate communications from your PC.

Link to comment
Share on other sites

Hi everybody,

 

I have still the same problem, I will try to ping the PLC as Alexander said.

 

Anyway, anybody know how to create a timer/pulse, I do not know If I should use a pwm.

 

I have 2 states for a sounder:

 

1- Continuous sound

2- Intermitent sound

 

The continuous is obvious, but no the intermitent, so what I am trying to program is a intermitent pulse when some swith is on

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...