Power Supply Wiring

Recommended Posts

Should I be grounding the power supply 0V. The wiring guidelines for the modules suggest that it should be earthed. I have seen many arguments for and against

Share this post


Link to post
Share on other sites

Should I be grounding the power supply 0V. The wiring guidelines for the modules suggest that it should be earthed. I have seen many arguments for and against

I never do it (since 2001 and a lot of Unitronics PLC installed that way in that time) and still not having a problem. But that´s just my personal experience. This is your first project?

Share this post


Link to post
Share on other sites

No, not my first project. I have not been grounding the 0V either but noticed the other day when testing my program with a 4-20 calibrator that my inputs were sweeping up and down, about 1/2 mA total. My calibrator output is rock solid since I checked it with a separate meter. When I grounded the 0V on the power supply the sweeping stopped and the input was rock solid. I guess its dependent on the bonding in the building the PLC is installed in and I should handle it on a case by case basis?

Share this post


Link to post
Share on other sites

No, not my first project. I have not been grounding the 0V either but noticed the other day when testing my program with a 4-20 calibrator that my inputs were sweeping up and down, about 1/2 mA total. My calibrator output is rock solid since I checked it with a separate meter. When I grounded the 0V on the power supply the sweeping stopped and the input was rock solid. I guess its dependent on the bonding in the building the PLC is installed in and I should handle it on a case by case basis

You need to have a good earth on the system. That´s all I check, if the earth is not a good one, then problems with analog signals are normal.

Share this post


Link to post
Share on other sites

I usually connect 0V to ground because it makes troubleshooting easier - clip the negative of your meter to a DIN rail and you can poke around with the positive lead.  

+1 on what HigHTech says - make sure you have a really good earth ground or you'll have problems with your analog signals if you ground the DC power supply.

Joe T.

  • Upvote 1

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...