Display

Recommended Posts

When I connect remote operator with Vislogic (PLC program), I lost all details on display. Please check the attached picture.

I run remote operator on different version of Windows (XP, Win7) on DELL notebooks. All failed. Any suggestion?

I run it on one PC with Win7 (Chinese version), it is ok.

it is better to send one email to me: rockysq@hotmail.com

thanks

 

F1.jpg

Share this post


Link to post
Share on other sites

Hi Rocky, you need to create the image cache file.  It then gets stored on the local PC.  With the PC that is working OK you (or someone) must have created the image cache on a previous occasion.

Share this post