I am kinda new to using visilogic and modbus. I just kinda need a better understanding of how to program using modbus to control this drive. Drive is allen bradley powerflex 4

Looking for a simple program to increase and decrease speed on the drive. Figuring on how the address part confuses me. Any example would help me understand little better

Thanks

 

Link to comment
Share on other sites

  • MVP 2023

Look at the existing Modbus examples to see how the function blocks go together.

It looks like you can talk to the drive using Modbus rtu via RS 485.  Look at this document starting on page C-2 - 

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/22a-um001_-en-e.pdf

Have you done any type of Modbus before?  It's not the simplest thing to do in Unitronics if you don't have a firm grasp on the Modbus protocol .  You may want to look at my post at the bottom of this thread:

http://forum.unitronics.com/topic/3582-modbus-rtu-and-danfoss/

Joe T.

Link to comment
Share on other sites

1 hour ago, Joe Tauser said:

Look at the existing Modbus examples to see how the function blocks go together.

It looks like you can talk to the drive using Modbus rtu via RS 485.  Look at this document starting on page C-2 - 

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/22a-um001_-en-e.pdf

Have you done any type of Modbus before?  It's not the simplest thing to do in Unitronics if you don't have a firm grasp on the Modbus protocol .  You may want to look at my post at the bottom of this thread:

http://forum.unitronics.com/topic/3582-modbus-rtu-and-danfoss/

Joe T.

I have no knowledge of modbus. Besides watching the videos from Unitronics. Was wondering how the addresses are applied into the ladder logic. But I will look over, what you given me. 

Link to comment
Share on other sites

  • MVP 2023

For MODBUS addressing, go to the Help file in VisiLogic, click on the Contents tab, then expand the following: Communications / Communications FBs / MODBUS, then select any of the topics you need to read up on. For addressing from an external MODBUS master, select Slave Addressing.

Link to comment
Share on other sites

Rog,

attached is an example of MODBUS control of an AB Powerflex,.....

I cut this portion out of a program I did a year or so ago, parts of the logic may seem gibberish, like anything else , there are many ways to do the speed and/or run logic, but the key to the comms is is sending the right number to the right address, look at the parts where I send/receive with the MODBUS FB's.

I added some comments in CAPS, pointing out some things to pay attention to......

also remember, the port on the V570 must be set to 485....... and of course, the baud  in the com init, and node settings in the MODBUS FB have to match the VFD.......

Hope this helps.

Regards, JohnR

 

powerflex VFD example.vlp

Link to comment
Share on other sites

27 minutes ago, JohnR said:

Rog,

attached is an example of MODBUS control of an AB Powerflex,.....

I cut this portion out of a program I did a year or so ago, parts of the logic may seem gibberish, like anything else , there are many ways to do the speed and/or run logic, but the key to the comms is is sending the right number to the right address, look at the parts where I send/receive with the MODBUS FB's.

I added some comments in CAPS, pointing out some things to pay attention to......

also remember, the port on the V570 must be set to 485....... and of course, the baud  in the com init, and node settings in the MODBUS FB have to match the VFD.......

Hope this helps.

Regards, JohnR

 

powerflex VFD example.vlp

Thanks. It does bring  in more perspective.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...