Capa_Anthony Posted June 13, 2017 Report Share Posted June 13, 2017 Hi, I configured the PLC as an Ethernet/IP adapter but I don't understand how to link tag to input/output when I configure the PLC as an adapter for Ethernet/IP. for exemple, my input_0 on the UID-W1616T (alis: Start_Process), how can I link it to the input tag created in adaptater node. If someone have a program explemple, it's can help me I have watch the tuto on Youtube but this parts is not explain. PS: It's the first time I use Ethernet/IP on a PLC. Thank. Quote Link to comment Share on other sites More sharing options...
Ofir Posted January 23, 2018 Report Share Posted January 23, 2018 If you wish to link the IO data to your Ethernet/IP configuration - just click on the green "Empty" of the Input or output to get the list of the tags in the system. In the list you will find also the UID-W1616T - Now you can choose it and select the inputs or outputs, if you wish to link the whole array just use the back space to delete the bracket and press enter. Quote Link to comment Share on other sites More sharing options...