MODBUS to Powerflex issue


Recommended Posts

Hey All,

Just ran across a quirky little thing while working on a new project,
I'm wondering if anyone else has experienced this.....

I'm doing MODBUS control of an AB Powerflex VFD , and mind you this is not my first experience doing this, I've done several projects using V570's, and usually do not run into problems.

This time I'm building some controls around a V120, and I am having an issue reading the speed feedback (frequency) from the VFD.

I've compared my logic to a previous project (logic looks the same, only difference is the MI's used in the RHR FB), and even set up two PLC's on my workbench (V570 & V120), and hooked up each to the same VFD to test.

Problem I have is that when the net is true, I get the correct reading, but when the net is not true I get some other number in MI 13. I have searched MI 13 and it shows it only being used in the RHR FB and on the display.

5984524d190f4_MI13search.PNG.598618270d8c399a7454af05ceb85667.PNG

I have slowed down my index to 1 Sec per step so I can see it in debug, and find that if I unplug my MODBUS cable while The net is true, then MI 13 stays put even after the net goes false, so it doesn't seem that the funny number is being driven by something in the program.

 

V570 reading speed feedback of 60Hz

598452710f131_570modbus.PNG.37d0faf964f3555db87ac78478e17275.PNG

V120 reading speed feedback of 30Hz when the index equals in that net

598452a3903e5_120modbusequal.PNG.2931af38d6c57c647f49f1403a231ca2.PNG

V120 reading something else when the index does not equal in that net

598452cbc1686_120modbusnotequal.PNG.29303ccbd21a7cd1c5c36d957b275453.PNG

I'm starting to wonder if it has something to do with Enhanced Vision vs. Standard Vision?

Any thoughts?

Regards,
JohnR

Link to comment
Share on other sites

Hi John,

Are you doing any Vector Fills or Copies where the index starts below MI 13 and the length is causing MI 13 to be over written?  The find function will not show MI13 linked to the Vector Copy or Fill if it's is part of the MI's in being written to due to the length of the vector.

 

Cam

Link to comment
Share on other sites

  • 1 year later...

here"s a little "Modbus Checker" program that I use with a V120 for testing Modbus controls to A-B powerflex VFD's

You can dissect this and see how the Modbus is done in Vision

Of course there are some hardware settings also,
you must set the jumpers in the V120 to make port-2 RS485
and set the powerflex to run on modbus

you will also need a cable going from RJ-11 to RJ-45
I don't have the pin-out in front of me but I'm sure it's easy to find...

JohnR

V120 PowerFlex.vlp

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...