Ethernet/IP to OMRON PLC


DanT

Recommended Posts

HI;

 

Customer has to Ethernet/IP into an OMRON Safety PLC.

We have the EDS file (NX-EIC202), and can make the connection and get the Basic Parameters.

The issue is setting up the T2O    and O2T  Assemblies and Structs for the Global Variables.

( we have done Ethernet/IP Setups for Bar Code Scanners and MURR IO Blocks  sucesfully,)

We cannot locate the relevent data in the Omron Information.

Information, experiences would help.

 

Dan

Link to comment
Share on other sites

  • 4 weeks later...

Hello All.

The application Dan references above is using the Unistream as an Ethernet/IP master to an Omron NX-EIC202 Ethernet/IP Coupler, which has a Safety CPU and a number of safety I/O "slices" attached.

Parameters ended up as follows:

Input Assembly 100

Output Assembly 148

Configuration  199

Leave both Run Idle check boxes UN-Checked

Leave Config Size empty

Leave Multicast checkbox UN-Checked

 

I don't really know much about EDS files and I got fooled by viewing the EDS file for the NX-EIC202 in notepad, and after seeing the following, used 150 instead of 148 for the output ass'y

"Param2,Assem150,       $ O->T RPI, size, format
 ,Param1,Assem100,       $ T->O RPI, size, format"

Hope this helps anybody/everybody escape the time consuming trial & error approach I went through.

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...