Boolean to HMI


MWD

Recommended Posts

I have a table that I store the current Boolean state of inputs 0-7.  My table updates fine with the date, time, input name and Boolean state of all inputs.  I can't figure out how to display the Boolean results in the table in a 00000000 format on the HMI.  

I am doing a table read from row 0 moving the Boolean field to MI15. In the HMI display, the start of the vector is MI 15 for 8 and I get no results on the display.

What am I missing?

Thanks in advance for your help.

Link to comment
Share on other sites

  • 1 month later...

Hello,

Basically you can first use Bit to Num ladder element to store the inputs array into a integer register.

Then write the value of the register to the data table.

Now in the data table you can right click on the cell of the integer column - select format:

image.png

Then choose Binary:

image.png

Now your column will be shown as Binary format on the HMI.

Link to comment