John.11 Posted April 3, 2018 Report Share Posted April 3, 2018 Hi I have a problem that my analog input does not go above 2.5 Volt and i need it to go from 0-10 volts. i will show you below my linearsation below and i wish someone could help me. Quote Link to comment Share on other sites More sharing options...
sgull Posted April 3, 2018 Report Share Posted April 3, 2018 Hi John What are you connecting your input into (PLC type or module type). Not all have the same range (0-16383) Regards Denis Quote Link to comment Share on other sites More sharing options...
John.11 Posted April 4, 2018 Author Report Share Posted April 4, 2018 Hi Denis Thanks for your reply, my PLC type is V1210 and the module type is V200-18-E3XB Regards John Quote Link to comment Share on other sites More sharing options...
MVP 2023 Ausman Posted April 4, 2018 MVP 2023 Report Share Posted April 4, 2018 And a clarification needed please. Have you actually measured the input volts at the terminals? When you say: On 04/04/2018 at 2:08 AM, John.11 said: my analog input does not go above 2.5 Volt that implies it actually doesn't physically do this. cheers, Aus Quote Link to comment Share on other sites More sharing options...
sgull Posted April 5, 2018 Report Share Posted April 5, 2018 As Aus said check that you actually have 10 on the input. Also check that you have selected 14bit and not 12bit on the mode tab of the hardware configuration. finally check that the snap in module is powered with 24vdc. Regards Denis Quote Link to comment Share on other sites More sharing options...