3 VFD-s on Modbus RTU

Recommended Posts

I can't configure program for 3VFD-s on MODBUS  485 RTU protocol.  PLC comunicate only with first one. depending on what I call the first one.

I try with all three in the first place and everyone is doing this, which means that the parameters are correct in them.

I know the PLC can only communicate with one at a time but I do not know how to write it.

 

V1210 and 3 VFD-s -MODBUS RTU.vlp

Share this post


Link to post
Share on other sites

Hi Dub

In net 8, 14 and 20 you are constantly writing to all 3 drives drive at the same time when MB0 is off.

I think you should put a delay on this and make a condition where you set a bit to communicate with the first drive and reset it after communication has finished.

Use this bit to prevent communication with the other drives until this is complete (same as what you did with MB5 in net 3)

Regards

Denis

 

Share this post


Link to post
Share on other sites

Hi Dub

In rung 7 for example you are resetting MB7 once the action is complete.

A normally open of MB7 should be in the same net before the modbus command to prevent it from being continuously called.

Similiar to rung 10

Regards

Denis

 

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...