qassim93 Posted June 21, 2018 Report Share Posted June 21, 2018 Greetings, I'm new to this form and to Unitronics PLCs and I would like to ask for some help/ I previously programmed "allen bradley" PLCs using a software called "RSLogics". The were 4 programming languages that I can use to build the PLC program. However, VisiLogic doesn't have "Structure text" language. I already have done the analog conversion using formulas and created the HMI, but I'm stuck now The program that I am trying to make is simply as follows: A number is written using the HMI and stored in a variable. This number is then compared to analog reading of the pressure sensor. If the numbers were different, then one analog output will be changed to reflect the number entered using the HMI - which will control a pressure regulator. Could anyone please help me with this issue ? Many thanks, Qassim Quote Link to comment Share on other sites More sharing options...
MVP 2023 Ausman Posted June 21, 2018 MVP 2023 Report Share Posted June 21, 2018 Greetings Qassim, basics first please. For both the pressure regulator and the pressure sensor, what types of signals do they work with? 0-10 V? 4-20ma? PWM? What PLC & I/O are you using? Can the system mechanically tolerate immediately changing to the new setting, or does it need to ramp? cheers, Aus Quote Link to comment Share on other sites More sharing options...
MVP 2023 Joe Tauser Posted June 22, 2018 MVP 2023 Report Share Posted June 22, 2018 You need to close the loop. It sounds like you want to enter a new pressure setpoint. You have no guarantee that adjusting the analog output by a certain amount will result in the pressure you want. Rather, you need some code that will adjust the analog output accordingly until the pressure is equal (or close to) the number entered on the HMI. This could be done with a PID block or some simple compare blocks. Post the PLC ladder program (the .vlp file) that you've worked on so far so we can see the hardware you're dealing with the the scaling you've done. Joe T. Quote Link to comment Share on other sites More sharing options...
qassim93 Posted June 24, 2018 Author Report Share Posted June 24, 2018 Hi, Many thanks for the reply @Ausman & @Joe_Tauser. I spoke to the guy responsible for the project and it turned out that he was mistaken. There is no set point required by the user. The functions looks like a simple linearization. The pressure read by the pressure sensor will directly drive the pressure regulator with a given formula. Currently I'm trying to create this simple program. But since I don't have any experience in using this program, I think it will take me some time to learn it. Many thanks, Qassim Quote Link to comment Share on other sites More sharing options...
MVP 2023 Joe Tauser Posted June 24, 2018 MVP 2023 Report Share Posted June 24, 2018 Here's what you/we need to know for this application, regardless of whether it's a Unitronics or Allen Bradley PLC- 1. The range of the pressure sensor and it's electrical output - 4/20 mA, 0-10V, 0-5V, or other 2. The model number of the analog input module or PLC it's connected to - required to determine the number of bits in the A/D 3. The "given formula" in detail 4. The model number of the analog output module - once again, the scaling code will be dependent on the module's D/A On 6/21/2018 at 4:17 AM, qassim93 said: VisiLogic doesn't have "Structure text" language. It sounds like the majority of your challenge will be learning how to program in ladder. Actually, very few of the small PLC manufacturers have spent the time, money and effort to conform to IEC-61131-3, regardless of what you read in the online trade articles. There's a reason why Visilogic is a free download and RSLogix 5000 is a $3,000 US software package, with an $800 US annual support subscription. Take a swing at it and post your code. We will do the best we can to help. Joe T. Quote Link to comment Share on other sites More sharing options...
qassim93 Posted June 27, 2018 Author Report Share Posted June 27, 2018 Hi, Many thanks for your reply Joe The PLC model I'm using is "Unitronics SM43-J-RA22". I will answer the questions you listed and we need to know their answers: the range of the pressure sensor is from 2 - 30 Psi(abs). Its sensitivity is 3mV/psi. Full scale span is 90mV. The analog input of this PLC 14bit (16384units). Its Input is set to 0-10v. The analog output is 12bit - from 0-10v. The relationship between the pressure sensor reading and the output that will drive the pressure regulator is pretty simple: the pressure reading will be from -0.5Bar to 0Bar. and the pressure regulator should start at 3Bar @ (-0.5Bar sensor reading) and ends at 0Bar @ (0Bar sensor reading). I used "Linearization" block to create the relationship between the pressure sensor input and pressure regulator driving output - as shown in the figures below. BR, Qassim Quote Link to comment Share on other sites More sharing options...
MVP 2023 Ausman Posted June 27, 2018 MVP 2023 Report Share Posted June 27, 2018 I don't think you are going to need it, but keep in mind that you may need to have further ladder work to set max and min outputs from the Linearization. It may not be a problem, but unless you do this the output numbers will keep on being done, regardless of whether they are outside the control span you need. This is an annoying quirk of Linearization that if needed, needs to be factored into every use by using compare blocks. cheers, Aus Quote Link to comment Share on other sites More sharing options...
qassim93 Posted June 28, 2018 Author Report Share Posted June 28, 2018 Thanks for your reply @Ausman I removed the linearization block - because I cannot use float and created a formula instead. The attached image shows the way I did it. I will test the thing and post an update about it. BR Quote Link to comment Share on other sites More sharing options...
sgull Posted June 28, 2018 Report Share Posted June 28, 2018 Hi Qassim If you want to use the linearization block just use MI or ML without the decimal place. For example if the input range is 15.25 to 95.35 just use 1525 to 9535. When it comes to display the result use the input screen to determine the decimal position. Regards Denis Quote Link to comment Share on other sites More sharing options...