good afternoon , we have a question about the following fuctionality Toggle coil ,  if we have  contact with positive transition rise   P ( from Key 2 from  front panel ) as you know when we push it we select the key 2 button from controller 120 R22  it would generate a pulse , at the first time when we do that , the toggle coil (x) result would be 1  and this value would be kept  until ,the second time  when we push  agan the keypad 2  then  the toggle result (x) would be 0  , Is it correct ?  

Please see the attachment here we show the configuration 

TOGGLE LOGIC.gif

Link to comment
Share on other sites

  • MVP 2023

Not quite.  You've reference TD 0 but not activated it using a coil assigned to the timer's address.   Also the Toggle coil will toggle on and off every other scan because you're continuously triggering it.  Always use a P contact with a keypad bit and with toggle coils.

You don't need MB 0.

I think this is what you're looking for-

image.png.a93a78883a1686df261be652a960639e.png

The timer will reset itself when you remove power (net 2).

Note that if you press Key #2 again while the bit is ON and the timer is running then you will toggle the bit off.  If you want it to stay on, replace the toggle coil in net 1 with a SET coil.

Joe T.

 

  • Like 1
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...