John_R Posted May 31, 2019 Report Share Posted May 31, 2019 Hey All, I have a possible upgrade project coming up, replacing some old automation direct plc/touchscreen controls. my first plan was to use a V570 (or V700) and do my I/O expansion rack style so I can have the HMI in the panel door and put my I/O a couple foot away without re-routing (much) existing wiring. But, now I'm thinking of going UniLogic/UniStream, a bit overkill for the project, but would be my introduction into this product line. I've played around with UniLogic a bit but haven't yet built a real project. I've been going through the hardware aspect on Unitronics Website and think I got it figured out but thought I'd throw this out to the forum community to double check my thinking. the existing project consists of; 20 digital inputs (sinking) 18 relay outputs 10 analog in 2 analog out So going through the Uni-I/O list I come up with the following modules to cover my needs: (2) UID-W1616R to cover my digital ins and relay outs (1) UIA-0800N for 8 of my analog ins (1) UIA-0402N for 2 more analog in and 2 analog out then it looks like I need; (1) UAG-XK125 Uni-Local expansion adapter (1) USC-P-B10 CPU-for-Panel (1) USP-070-B08 HMI Panel Does this look correct, or am I missing something? Regards, JohnR Quote Link to comment Share on other sites More sharing options...
MVP 2023 Joe Tauser Posted May 31, 2019 MVP 2023 Report Share Posted May 31, 2019 That's cutting it awful close on analog I/O counts. You've picked modules that will work, but you've left yourself no room. I would keep your analog ins and outs separate - (2) UIA-0800N (1) UIA-0006N Room to grow. Any of these inputs thermocouples? Joe T. Quote Link to comment Share on other sites More sharing options...