Recommended Posts

Is this a UDFB? If so, keep in mind there is no retained memory of local variables after a UDFB executes. Transition contacts require retained memory in order to know a transition occurred.

Share this post


Link to post
Share on other sites

OK. How to organize the processing of the algorithm along the rise and fall inside UDFB? The structure in the image continues to be processed in a loop, even after setting the ON bit. I mistakenly inserted a coil instead of a contact, but even if there is a contact, the circuit repeats itself cyclically until the Alarm.Active bit is true