sm 70 -j-RA22 analog input shows 32767
  • MVP 2023
According to the Technical Spec sheet, that is an error code that means the input is greatly above the input range (i.e. it's measuring greatly above 20mA on the input). Check your wiring and make sure the connections are correct and there isn't a short.
You don't mention the minus side of the power supply. It should be connected to the common terminal of the analog input.