Maximum expansion IO modules per adapter

Recommended Posts

I seem to have bumped to an undocumented limitations on I/O expansion module count per adapter (EX-A1 or EX-RC1).

The hardware configurator allows us to place 8 ATC8 modules on the rail without error. (Also, note that with 8 ATC8, the 5Vdc power limit is not exceeded). However, we get an error message when we try to configure the entire 64 channels available.

post-99-085470300 1307314615_thumb.jpg.

The error start to appear on the 50th channel. Actually, when mixing a combination of digital and analog I/O modules, the limit appears to be 50 words.

If 50 IO words is actually the limit, then it should appear on the documentations as it is an important information for sizing the PLC.

We need the entire 64 AI channels per rail. Is there any work around aside from adding another adapter module?

Thanks.

Share this post


Link to post
Share on other sites

Hi,

Unfortunately, there is no workaround this limitation. You need to add another adapter.

Note that there is an indication of the IO Capacity at the bottom of the Hardware Configuration window.

Share this post


Link to post
Share on other sites

This limitation (actually there is possibility to use only 49 analog I/O points) MUST be mentioned in documentation and brochures. So the V1040 and V1200 MUST have more I/O capacity, 49 I/O words is not much. There is 64 I/O words needed!

Share this post


Link to post
Share on other sites

Two notes:

1. "Limitation" CANNOT be metioned in any documentation, as it depends on many factors. This number comes from limitation in communication between PLC and EX-A2X. As Yair stated in his post above, in bottom line of Hardware configuraiton window (VisiLogic) there is a "calculator" of communication load. Any one can check before starting to build his project.

2. In fact, there is no such limitation! You can add Remote adapters EX-RC1. To each adaprer you can connect, let's say 6 x IO-ATC8 = 48 universal 14 bit AI. You can connect up to 60 x EX-RC1 to one PLC. This means - 60 x 48 (via RC1) + 48 (on A2X). In my calculator the number is 2928. You can add another few analog I/O on board or Snap In module, but this will not change the final situaiton drastically.

BTW - having 6 x ATC8/AI8 ot each adapter, you can still add up to 2 more I/O modules with digital I/O...

Share this post


Link to post
Share on other sites

As I understand the issue, there is a 50 words limitation for local I/O expansión. 16 points digital input or output uses 1 word, so, one can mix any cards as long as they do not exceed such limit.

Am I correct?

 

I tried 6xATC8/AI8 + 1xIO-DI16 + 1xIO-TO16 and calculator shows 100% capacity, but also got same error of original post

Share this post


Link to post
Share on other sites

UniCAN can transfer 32bit at one package. In this matter you're right. But there is no problem to send thhe data in several packages. It will be slower, but if you transfer analog values, which don't change so fast, it will be more than good enough.

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...