Hello

I have a Samba PLC application, and have for the first time connected remotely to a Unitronics PLC via Remote Operator to demonstrate the functionality.  I received a request to have a status flag or icon of some sort on the HMI screen to notify the local machine operator that there was an active Remote Operator connection.   

I looked in the System Bits but didn't seen anything that directly addressed this; similarly  didn't see anything in the help files unless I'm just looking in the wrong spot because I don't know what to call it. 

 

thank you, 

 

Jeff

Share this post


Link to post
Share on other sites

I believe you should see SB 148 ON when you are connected with Remote Operator (assuming you are using the default Socket 1 for PC-PLC communications).

  • Like 1

Share this post


Link to post
Share on other sites

Thanks -  I had overlooked that.   There allot more System Bits than I was aware of,  I hadn't scrolled that far into the list.  