Jump to content

Samba SM43-RA22 and IO-D16A3-R16


Recommended Posts

Hello,

I have to add I / O on an SM43-RA22.
My supplier sold me an extension for can-open to be placed in the SM43, V100-17-CAN.
I also have an EX-RC1 module and finally the I / O module IO-D16A-R016.


Do you have a procedure for implementation?


I found that :
https://www.youtube.com/watch?v=APnEBvSqhks&list=PLFBq_OH6_be7snAZAycZzQMvAWjHkX9Pz
They use Visiologic and Unilogic but me my project is only Visiologic    ????????

Thank you for your help 

 

Pierre

Link to comment
Share on other sites

  • MVP 2023

I've never tried it out of the box, but you should be able to.  The network ID of the RC1 is set via the dip switches, and you can point Visilogic at it using the Communication settings dialog box-

image.png.3756a2e1fbc1c95fdf6c7ff355e0346b.png

The SM43 should work as a bridge.  Just remember to keep your programs and your com settings straight when you're going from one to the other.

Joe T.

Link to comment
Share on other sites

  • MVP 2023
10 hours ago, Joe Tauser said:

Just remember to keep your programs and your com settings straight when you're going from one to the other.

Pierre, in doing this you may like to try multiple instances of Visilogic which makes it so much easier.

cheers, Aus

http://forum.unitronics.com/topic/4015-multiple-connection-live-checking-tip/

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...