SCADA to PLC and PLC to PLC communications


Recommended Posts

This is absolute newbie question. Is it posible several VisiLogic PLCs to be Modbus slaves to SCADA master and the same PLCs to support Remote PLC DataCom. PLC and SCADA computer are physically connected by Ethernet. The reason for this is that I do not want exchange of data between PLCs to go via SCADA computer. I

Link to comment
Share on other sites

You can have multiple data connections as long as you have multiple communications ports. For example, the V570 comes with two RS-232/RS-422 ports standard, one expansion slot for another 232/422 or Ethernet, plus a CANBUS port. The CANBUS port can be used for PLC-to-PLC communications, and the serial ports can be used for SCADA-to-PLC connections. You can also use the Ethernet port for multiple simultaneous functions.

Link to comment
Share on other sites

You can also use the Ethernet port for multiple simultaneous functions.

Tank you very much for your clarification! As stupid newbie I should ask again. Does your statement above means that a Vision PLC could be master for another PLC and at the same time slave for SCADA if PLCs and SCADA PC are in Ethernet network?

Link to comment
Share on other sites

  • 1 year later...

Yes, you can establish up to 4 communication channels using Ethernet Sockets 0-3 with independent config setting and you can change configuration of each channel in run time.

i agree with linxchas. you can use ethernet sockets for up to 4 communication channels with independent configuration settings.

______________________________

Flotech Controls Pte Ltd - scada or supervisory control and data acquisition is a communication system solutions which provides management system integration. This is also using HMI configuration and controller hardware to support client needs and requirements.

Link to comment
Share on other sites

  • 3 years later...

Hey all,

 

I'm newb at this too. I have two plcs that need to talk to eachother. can they talk across a common router? one of the PLCs has a EWON router in the cabinet and the other has a switch. If so could anyone point me to an example of how to do it or at least some sort of start point.

 

Thank you

Link to comment
Share on other sites

  • MVP 2023

I regularly connect PLCs together to communicate data between them. I usually use MODBUS IP when connecting by Ethernet. As long as the PLCs are on the same subnet, they will communicate with ease and are reliable. You don't even need a router, hub, or switch if there are just two PLCs - just a crossover cable. There are example projects for Ethernet communications that come with your Visilogic installation. Go to Help\Examples\ and drill down till you find "V280_Ethernet_TCP_MODBUS_IP_Master.vlp" and "V280_Ethernet_TCP_MODBUS_IP_Slave.vlp". The functions are the same for all of the Vision products.

Link to comment
Share on other sites

  • 3 years later...

So let me see if I have understood the above correctly : I can set up master socket and a slave socket that will function in parallel?  In effect I will have a master/slave hybrid?

I am building a system with 10 Samba SM70-J-R20's each of which have a slaved autonomous vehicle with additional onboard I/O. 

I am using Modbus TCP/IP for communications over wifi. 

So far so good.

I also have a Vision 1210 which will act as a "god" and can take over and control the vehicle by writing bits directly to the Samba, and the Samba then does its thing.

Please see attached one line diagram

I have been wondering how I was going to deal with three layers, "Master-Master", Master and Slave, if I have understood correctly then I can set up the Samba as a hybrid and the system should work.

I would be grateful for confirmation that this will, or will not, work before I sit down and start playing in Visilogic.

Thanks in advance

 

one line.JPG

Link to comment
Share on other sites

  • MVP 2023

Your description is not precise enough to know if this will or will not work. However, I'll reiterate what was said above. Each V1210 & Samba PLC has 4 sockets for ethernet communications. Each socket is one communications channel to communicate with one device at a time. Each of these sockets can be setup independently as master or slave to any 4 ethernet devices simultaneously. You cannot maintain simultaneous communications with more than 4 devices using MODBUS TCP from any single PLC. You can, however, communicate with up to 4 of the Sambas from the V1210, while having each of those 4 Sambas communicate with up to 3 other Sambas in any way you wish.

Link to comment
Share on other sites

Hello Flex, thanks for the rapid answer.

I will try to be clearer.  Each Samba / vehicle pair are stand alone and do not communicate with any other pair.  A simple master/slave setup using a single port

Occasionally, I want the vision to be able to read or write to one / several / all of the Sambas  e.g. send a start or stop signal to all of them at the same time (or in very rapid sequence)

If I set up one socket on the Samba as a master,  and a second socket slaved  to the Vision, I should be able to achieve this.

The vision can then be programmed to address messages to each samba in sequence.

Or at least that's what I was planning

Link to comment
Share on other sites

  • MVP 2023
1 hour ago, Patrick said:

The vision can then be programmed to address messages to each samba in sequence.

Yes, but be aware that the process of disconnecting the V1210 from one Samba and connecting to the next can take time, maybe a couple of seconds. If speed is of the essence, then have the V1210 stay connected with up to 4 Sambas, and have those Sambas stay connected with all the others, and have them relay the message. That can happen very rapidly (probably less than 100 or 200 milliseconds, perhaps much less).

Link to comment
Share on other sites

  • MVP 2023

Perhaps this will flesh out more what I was trying to say:

V1210 Master to Samba 1-4

Samba 1 is slave to V1210, master to Sambas 5 & 6

Samba 2 is slave to V1210, master to Sambas 7 & 8

Samba 3 is slave to V1210, master to Sambas 9 & 10

Samba 4 is slave to V1210 only

This still leaves an open socket on each of your Sambas and allows very rapid communication to all the Sambas from the V1210 (with the right code in each Samba).

Another consideration (still doesn't solve all problems, but makes things a little easier) is the V700. It has 8 sockets instead of just 4. And finally, the UniStream has unlimited sockets, so that is another option.

Link to comment
Share on other sites

Hmmm.

I had not taken into consideration the time to connect and disconnect, although it is quite speedy on the test units I have.

The only problem with the relay idea is that if (for example) Samba 2 is switched off for maintenance then the message will not be passed along.

I have already purchased all the hardware, but considering the above I will get a quote for a Unistream tomorrow.  That seems to be the only way of doing this without a complete rethink unless you have any other ideas?

 

Link to comment
Share on other sites

  • MVP 2023

If your test setup runs fast enough for you, then that's obviously better info than my estimate.

The right code can overcome one of the Sambas being off, but the permutations might get overwhelming.

A UniStream will definitely be able to maintain a MODBUS TCP connection to 10 Sambas simultaneously.

Link to comment
Share on other sites

I did, and decided on TCP/IP because it is faster.  Oh the irony !

I could still buy 10 serial ports for the Sambas I suppose, but that would cost me half the price of the Unistream, plus I have already pulled all the Cat6 and I would lose the ethernet port.

On the other hand I also have CANbus cards for the Sambas in stock as I was planning on using them for something else, and then changed my mind.  Could I use CANbus between the Vision and the Sambas?

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...