Sign in to follow this
Benja
UnCmDrv1.dll
Hi there,
I'm working with V130 and ethernet card, i want to make a SCADA in VB6 with ethernet communication. I tried direct comm and it works, but i'm lost with the ethernet communication ¿What FBs i need to set in the ladder program? ¿I must set the PLC as Modbus IP slave?
Would greatly appreciate your help.
Best regards.
The function calls for this driver are not very well documented. They usually try to push everyone off on the .NET version.
On the ladder end, all you need is PLC Name FB, a TCP/IP CARD INIT FB, and a TCP/IP Sock INIT FB.
I am going to give you some good values you start with. I should stress that you don't necessarily NEED to do it exactly as I have, but it will match well with the example I am giving below.
Name the PLC "V130"
Init the card to whatever IP address you want.
My example used
IP: 192.168.1.10
Subn: 255.255.255.0
GTWY: 192.168.1.254
Initialize socket #3 to
TCP
Port D# 20257
Slave
Put all three of these FBs in the first network of you main ladder all in series and triggered by the SB2 contact.
That is all you should need to do on the ladder end for base communication.
If you leave socket#2 at default, you will be able to also continue to use Visilogic on port 20256 so that you can do both simultaneously.
Downloading programs over Ethernet is much faster than RS232, so since you will have an Enet card on this anyway you might as well take full advantage of it.
Anyhow, with that being said, here is a sample function in VB to invoke an Ethernet connection.
You can ignore the parts that are related to serial comms.
Private Function prvOpenPort() As Boolean
Dim eComParam As tPC_CommSettings
Set mComDriver = New UnCmDrv1.clsCommDriver 'Create a new instance of Unitronics CommDrive DLL
'Configure the connection parameters.
With eComParam
.Baudrate = eBR_38400 'baud rate
.DataBits = eDB_8 'data bits
.Parity = eP_None 'parity
.StopBits = eSB_1 'stop bits
.TimeOut = 500 'communcations timeout
.Retries = 3 'number of retries
End With
With mComDriver
.Comm_Autodetect = True
.ShowCommMessages = True
.Comm_TimeOut = 10000
.Comm_Retries = 3
.Ethernet_Protocol = UnCmDrv1.enEthernetProtocol.eEP_TCP
.Ethernet_RemotePort = 20257
.Ethernet_RemoteIP = "192.168.1.10"
If Not .Ethernet_Connect Then
MsgBox ("Com Open = False")
End If
End With
mComDriver.Comm_Autodetect = True
mComDriver.ShowCommMessages = True
prvOpenPort = mComDriver.Ethernet_Active
End Function