  1. First off, if you're receiving 6 digits you'll need to link to an ML, not an MI. Try changing MI 285 to ML 0 in your variable definition block and see if that works. I've had trouble with the scan block doing the numeric receiving and translation in one operation. For testing, try changing your input variable to a straight longer-than-needed Stream type and see if you can grab the control characters as well. They may not be sending all six characters as weight. Here I've set up the block to receive a stream of any kind that hits the COM port up to 10 characters. The incoming data