  1. Maybe best solution https://www.geckodrive.com/support/using-current-source-plc.html
    1 point
  2. Nothing to do with controllers or odd misinterpretations of binary digits, but one of the funniest things I've seen in a while. Put down your coffee. You have been warned!
    1 point
  3. 1. Delete MI 8 power-up value -Sample Time. It will be calculated by Autotune. 2. Water temperature range is 0 to 100. It is recommended to set: - MI 9 =0 (0.0) - MI 10 = 1100 (110.0) 3. MI 0 show temperature in 0.1 C/F. 4. Change User Set point MI 47 format to 4.1 Entering 55.1 from display will be represented as 551 in MI. 4. Use MI 47 instead of MI 3. 5. Sample MI 0 in 4.1 format. 6. Delete nets 2 and 3. Test it.
    1 point
  4. That's actually a program crash within the PID server. It's been a long time since that module has been updated. What happens if you Auto Tune the loop without it? Joe T.
    1 point
×
×