  1. You can create a struct that contains the information structure that you want to pass to the UDFB. It is more logical to pass a struct with 50 members other than passing 50 inputs. Think of how the ladder element that accepts the 50 inputs will look like. it will start at the benining of the screen, and you would have to scroll few pages down in order to see its end.
    7 points
  2. Download the attached Rar file, and extract the files to UniLogic installation directory. This means that the "UniLogic Diagnostics.exe" (and all the other files) must be placed in the same directory where "Unitronics.Shell.UI.exe" is located (usually at: "C:\Program Files (x86)\Unitronics\UniLogic\") After you've extracted the files, run "UniLogic Diagnostics.exe" and click on Diagnose. Most chances that it will show "SQL Instance" as one that has problems. In case it find problems, the "Fix" button will become enabled. Click on Fix, and the program will attempt to fix the pr
    6 points
  3. EDIT BY MODERATOR: Kikis CAN NO LONGER SOURCE THIS UDFB, SO THE POST IS BEING REMOVED BUT THE LABEL RETAINED IN CASE SOMEONE IS REFERENCING IT SOMEWHERE.
    4 points
  4. If it is really bad I've been known to hang an electrolytic capacitor between the analog input and 0V. I'm not kidding. Something like 10 uF @ 25V. Joe T.
    4 points
  5. The USB in the UniStream acts as an Ethernet card (while in Vision PLC, it acts as a serial port). The USB of the UniStream is an RNDIS device, and for getting // assigning the IP address of the PLC over the USB-Ethernet an uPnP protocol is used. If the firewall blocks the uPnP handshake between windows and the PLC, then UniLogic will not be able to get the IP Address and communicate with the PLC.
    4 points
  6. Sadly not my joke....... My wife asked me why I was whispering in the house. "Because Mark Zuckerberg's listening," I whispered. She laughed. Alexa laughed. Siri laughed. 🙈 cheers, Aus
    3 points
  7. I think most of you probably already know the first rule of the Assumption Club.
    3 points
  8. Twitter asks what I'm doing. Facebook asks what I'm thinking. Google asks where I am. The internet has turned into my mother. 🕵️‍♀️
    3 points
  9. 3 years ago I knew nothing about PLC's. Because of people like @Ausman, @Flex727, @Joe Tauser and others on this forum, we converted 8 machines from old relay logic to PLC's with automation, made 2 pieces of complex laboratory test equipment for the lab, and entire tank farm controls that include, levels, filling, heating/cooling, mixing etc. I could have never done it with their help. I don't know if they're paid or not, but I will tell you they are priceless. I hope that @Cara Bereck Levy will show this to the powers at be so they understand the caliber of people they have in this foru
    3 points
  10. Yes, it was already implemented and would be available on the next release of UniLogic.
    3 points
  11. Just for fun, this is the control panel for a new force tester we created. If you are a Star Trek fan. I can't be the only nerd on this forum, am I?
    3 points
  12. 3 points
  13. Hi All I purchased this device on ebay. The model number is "VAP11G Bridge Cable Convert RJ45" (probably many alternatives available) Cost around €15.00 Works a treat on unistream. Plug in the ethernet and power via the USB port. PLC can now be programmed with the panel door closed over wifi. Should also work with Vision but you would need a power bank or 5v power supply.
    3 points
  14. Continuity is easy - just connect +24V to one side of the wires one at a time and see if you get it on the other side. If you have a bundle to check you can switch wire feeds in with relays and make sure you only get one signal on a DI module connected to all wires. The RTD module only returns temperature from a resistance of about 25 ohms to 267 ohms. You could reverse-calculate the resistance, but I don't think this is the range you're looking for. Resistance is not so easy. Many moons ago I rolled my own ohmmeter with a DC power supply, current limiting resistors, voltage input
    3 points
  15. Hold Ctrl+Shift while you double-click the Visilogic icon. This will reset the window settings to factory default. Joe T.
    3 points
  16. @Arnor, I think I've found the problem. Take the dll below and overwrite the one that exists in your installation folder. Make sure to create a backup of the original dll first. Please update me if it helps. Thanks. Unitronics.RemoteOperator.dll
    3 points
  17. I´m not sure if this fits your needs:
    3 points
  18. Almost the same here. The only difference is that I am using an accumulated timer for more precision:
    3 points
  19. I'm convinced this is delusional. CDs were originally pretty bad because sound engineers failed to properly tailor the sound for the new media and instead used the equilization curves for vinyl with insufficient modification. That's no longer the case. Nowadays, the abysmal compression of MP3s may be worse than vinyl, but no one who really cares about sound quality should be listening to either compressed MP3 or vinyl. Vinyl necessarily has extreme equalization in order to achieve any bass response, necessarily lacks sufficient channel separation, and degrades every time the record is played.
    3 points
  20. This major release introduces MQTT, another piece of the Industry 4.0 puzzle. MQTT is a machine-to-machine connectivity protocol that runs over TCP/IP. MQTT joins the UniStream range of communication channels and protocols that supply the connectivity required by Industry 4.0 including SQL, built-in webserver that enables the controller to be accessed via any browser, and more. This release also supports new UniStream 5” models US5-Bx-R38 + US5-Bx-T42, offering new, built-in I/O configurations. Other important features in this release: HID Device support for devices such
    3 points
  21. 3 points
  22. I've had a lot of local requests for help on getting email working. There are a lot of pieces needed to make it work right and it has to be done in the right order. A PLC was never invented to send emails, and the fact the Unitronics can do this is a pretty awesome feature. I'm posting a sample program we wrote to hopefully show everything needed and some tricks to make it cool. Joe T. Sample Email Program V570 5-6-15.vlp
    3 points
  23. Great news, but twice as tall (or 50% taller) is what I need more. I have regular need for 12 contacts in parallel and constantly breaking them into two sets of six is a pain.
    3 points
  24. What is the answer to this math problem: 7-1x0+3/3=? If you understand the PEMDAS rule you will get the correct answer of 8. However, if you just run the operations from left to right, you'll get 1. Every ladder rung in your program must be compiled to machine language before the PLC can execute the code. Do you know all the rules the compiler will use when you have a very large net? I certainly don't. Remember, like all computers, the PLC can only do one thing at a time and a large net can provide ambiguity (to humans) so the result can sometimes be unpredictable. To avoid this potential
    3 points
  25. Ohh no, the old usb issues! 1 Perhaps Win 7 is now doing the W10 trick of updating drivers to whatever Msoft deems best, regardless of what the user wants/knows. I'm still on 7 and haven't encountered this yet, but I very carefully look at every update that is offered and find what it is doing. The immediate suggestion is if you have System Restore on, you should roll back to before the updates and see what happens. 2 I have had instances where a usb cable has suddenly broken a line internally. I'm assuming you have tried another known good cable in your attempts? In my instanc
    3 points
  26. This problem dates back to when the USB to serial adapters were first introduced. It is not a Unitronics-only problem, it's a Windows thing. I have experienced multiple instances of the same driver trying to access the same COM port when it comes to the USB interface. It is a royal pain in the butt and you have to rip them all out and start with a clean slate. The problem is you can't see them all, even if you check "show non-present devices" in the Device manager. There is an environment variable you have to set to truly "Display All Non-Present Devices". This article describes
    3 points
  27. Set the Border Thickness to 0, and the Background Fill to transparent (by either choosing the transparent color, at the bottom left corner of the Stardard color, or by entering 00FFFFFF in the Advanced Color)
    3 points
  28. I would like to start with many compliments on the Unistream Product. Yes it is a huge cost savings from other comparable products out there, but the horsepower really comes to light when using the data tables, FTP interface and the USB DOK tools. Not only can you accomplish a lot of traditional tasks with these units, but you can work with data and share this data so easily. Thanks. There are (2) enhancements that I think go together that would put the icing on the cake. 1st, we need at least (2) dimensional arrays. You have sort functions for arrays, but with only a single dimension
    3 points
  29. So I am sure that some of you may know factoid 2 already but I decided I would share the benefit of lots of testing with everyone. In our products we use the V570, V350 and the JAZZ units to talk to variable speed drives on a regular basis. Most drives come standard with 485 Modbus as the only communications type unless you spend extra money getting optional com cards for the VFD. Two factoids relative to noise. There was a conversation that happened accidentally in the "I have a new project" topic where someone said that Unitronics was very susceptible to noise. Well VFDs make a large amount
    3 points
  30. Hello, I currenlty busy with a project Unistream 7" + 2x 8DI/DO and a EX-RC1 + 3xPT4x, 2x4AI2AO + 2xAO6. Followed the instruction on the webinar. What took me some time was that you have to upload a ladder programm with Visilogic to the EX-RC1. They don't show it in the webinar - because standard the EX-RC1 is pre loaded with a program - which has an auto configuration for digital inut and output. But when you want to use it for analogue input/output you should change it - by uploading the program in Visilogic withe the serial (9 pins) cable and RJ11 connector. When you follow the
    3 points
  31. Hello Active Just did a simple test with Kepserver and selected the ”Modbus tcp/ip driver” Channel properties=>Ethernet settings selected port 502 and ip protocol tcp/ip. Added a device and named it device1 and for the model selected “modbus”. ID <135.0.2.78>20 The V570 has this ip address and 20 is the slave number in my test situation. In the V570 socket init in my case socket 3 port number 502 and server(slave) followed by A Modbus ipconfig,selected in this function block socket 3 and gave it network id 20,time out 100 and retries 3 and assigned a function in progre
    3 points
  32. Receiving BMP file thru RS232 from fingerprint scanner and drawing it on the dispay: [media=] [/media]
    3 points
  33. Big time thanks to Joe for his support, even thuogh sometimes I bug him when I am in a crunch, he always comes thru with an answer.
    3 points
  34. A shepherd was herding his flock in a remote pasture when suddenly a brand-new BMW advanced out of the dust cloud towards him. The driver, a young man in a Broni suit, Gucci shoes, Ray Ban sunglasses and YSL tie, leaned out the window and asked the shepherd... "If I tell you exactly how many sheep you have in your flock, will you give me one?" The shepherd looked at the man, then looked at his peacefully grazing flock and calmly answered "sure". The man parked his car, whipped out his IBM ThinkPad and connected it to a cell phone, then he surfed to a NASA page on the internet where he called
    3 points
  35. Permanently run remote access or remote operator on the PC and tuck it away in a little used corner of the desktop? Or....have a look at UniDDE, or perhaps UniOPC https://unitronicsplc.com/Download/SoftwareUtilities/UniDDESetup_1_3_6.exe DDE will likely give you the basics of what you want, but you might need a little script running to cycle things periodically to fully achieve your needs. So you'd have a little excel window running and updating with just the info you want visible. cheers, Aus
    2 points
  36. At the end of program (at the end of every scan) copy those registers into some other free DWs. Then at startup copy them back, via SB2 contact. I think there should be a complete example of this method somewhere in this forum, I've seen this topic before.
    2 points
  37. @chay Seriously, dude, you are going to catch nothing but grief asking questions like this on the forum. This forum is maintained by unpaid volunteers. If somebody posts code showing that they have put the time in and tried to learn themselves we will bend over backwards trying to help them. Put the time in yourself. Then ask questions. Joe T.
    2 points
  38. When you’re all out of fuses but have plenty of ammo. Photo credit to Paul on the facebook “Emergency Lights and Sirens Enthusiasts” group.
    2 points
  39. Something tells me that @Joe Tauser's troubleshooting face is the same as his regular one.
    2 points
  40. Dan- You are really going to be freaked out when you realize Unitronics allows multiple coil stacking and curvy logic joints- If your primary focus has been the various flavors of RSLogix, I totally understand your irritation with the Unitronics way. After I originally read your post I considered the packages I've also programmed- AB SLC500 + uLogix, PLC 5, RSLogix 5000, Omron, Mitsubishi, Idec, Siemens, and the Modicon x84 series. As you state, it seems to be a toss-up as to rung-starting methodology. None of them were especially difficult to figure out with t
    2 points
  41. Are you talking about a DW or an ML operand? The value when the register overflows is slightly different (the ML will go to the max negative value since it is a signed 32-bit integer, and will count up from there). In either case, no error will be generated. −2,147,483,648 to 2,147,483,647 is the range for an ML (32-bit signed integer) 0 to 4,294,967,295 is the range for a DW (32-bit unsigned integer)
    2 points
  42. OK. Still confusion. I'm assuming you are talking about having your push button "1" connected to Digital Input (DI) 1. Then your button 2 on DI 2 and so on. This will use many of the inputs, which is OK if you have them to spare. You saying "port" in some ways means the serial connection socket, hence my question. There are other ways of doing this, but......... Before I go any further, have you considered using a cheap touch screen computer running Remote Operator, directly linked to the PLC? In some ways this will be the easiest method of the lot as you can use the inbuilt numbe
    2 points
  43. That description is subject to Israeli trademark number 049 115 116 032 065 112 114 105 108 033, and you need special permission to use it! ho ho. cheers, Aus
    2 points
  44. OK. 1 Have you tried another type of usb device in the same socket on the PC? Anything at all that previously worked ok. 2 In the same vein, have you tried using another socket on the PC? 3 Re the broken core, yes...it makes no sense that the system still recognises a plug insertion with one line down, but that's what happened, and happened a few times. I don't know the mechanics of the usb process enough. A new cable and away it went. I am not at all hard on cables, but I do know there are many different construction qualities out there! 4 Go back even further on
    2 points
  45. In a future release of Visilogic, it would be great if you could have the option to make the properties window permanently visible, perhaps on the right side. I use Visilogic alot, and this would save so much time from right clicking on an object (objects that bring up a variable window instead of properties window when double-clicking) and clicking properties. Not a big deal with small projects, but tedious for big projects with 100+ objects across multiple screens. If there's already a way to do this, someone let me know. Thanks.
    2 points
  46. Move those operand addresses FIRST before exporting.
    2 points
  47. Use "Legal Entry" in the HMI input to know when the timer has been updated. Then compare the Timer Preset with the min and max values you want. You can either reset the preset to the min or max value, or pop up a screen that informs the operator that they've made an error. The option you suggest does exist for numeric entries and I agree that it would be nice to have it for Timer inputs also.
    2 points
  48. Here is a sample program that has been split out of a much larger program. In it you will find where the user can enter in PID variables and the set point along with dynamically being able to chose if the pump PID is controlled from suction or discharge pressure. This is about the best I can do for you at this time. Good Luck Keith PID example.vlp
    2 points
  49. Hello, UniLogic able to support PNG images and VisiLogic doesn't support PNG properly as it converted into a bitmap in Vision PLC. PNG originally can be transparent so UniLogic don't need any dedicated tool. I hope it helps..