  1. Hi Juan, Following Ofir's questions above, can you please also update us the PLC's serial number? Please reply to support@unitronics.com Waiting for your updates. Thanks.
  2. Hi, The live update is already fixed in version V9.7.9. but any way check if he need to use Proxy or Internet Explorer download setting (see the image below). I hope it helps.
  3. Hello, Yes i familiar with cheap camera that works with UniStream: The camera model for the demo case is ELP-IP1881. Websites: www.elpcctv.com I hope it helps.
  4. Hi Please try to recover this issue as follow: · Download a blank project to your PLC by using COM port RS232 115200 baud rate. · Initialize and reset the PLC (all value will be cleared) · Open the original project · Restore system images (see below how to..) · Perform build-all from Build menu · Download all & burn the project to the PLC (again by using COM port RS232 115200 baud rate) I hope it helps.
  5. Hi, First, please make sure that the bus connector is properly attached to the CPU. If it does, Can you try to add another unit before this one and try again?
  6. Hello, Please contact support@unitronics.com
  7. Hi, The battery type to all models (except JZ20) is: RENATA BATTERY,COIN,2450,3V,LITHIUM http://www.renata.com/fileadmin/downloads/productsheets/lithium/3V_lithium/CR2450N_v06.pdf Unitronics part number: 160200362 I hope it helps.
  8. Dear Aus, Windows 10 is still new and we didn’t finish all our tests to give an official statement, only what is stated in our System Requirements. We successfully manage to run UniLogic , VisiLogic and U90Ladder under Windows 10.. Please note - JAZZ20 USB port driver currently is not supported by Windows 10. How to Disable Driver Signature Verification on 64-Bit Windows 8.1 or 10 To disable driver signature verification, we’re going to need to get into the Troubleshooting options from the boot manager. The easiest way to bring this screen up is using a secret trick. Simply select
  9. Hello, Note that you can always go to our web site www.unitronics.com and find more information under the support page>technical library. All Unitronics software's & Tools as well the support are FREE of charge. The main software's are U90Ladder , VisiLogic and UniLogic. VisiLogic – for Vision and SAMBA series U90Ladder – for JAZZ/M91 series UniLogic – for UniStream series U90Ladder / VisiLogic / UniLogic software's are available to download from our web site (FREE of charge) at: http://www.unitronics.com/Content.aspx?page=Downloads After installing the desired software go to
  10. Hello, it seems that the project is damaged. please send the project to support@unitronics.com. i hope it helps..
  11. Hello, UniLogic able to support PNG images and VisiLogic doesn't support PNG properly as it converted into a bitmap in Vision PLC. PNG originally can be transparent so UniLogic don't need any dedicated tool. I hope it helps..
  12. Hello, M210/M216/M218 and other controllers from Minicon M2xx series are very old. They was discontinued more than 12 years ago. We don’t support them anymore. We have no controllers in stock and, as most of electronic components were discontinued long time ago, we cannot produce or repair these PLC. I arranged for you some materials according to your request below, You can find the programming software and guides for these controllers at: https://unitronics.exavault.com/share/view/5rqf-5nv0ru29-6g1aovwl Programming cable: The programming communication kit is RJ11 4 wire cable a
  13. Hello, Please update the PLC to the latest system files (BinLib, Boot, O/S) using VisiLogic V9.6.0. Then Download a blank project and perform initializes & reset. If the problem still occur please contact support@unitronics.com for farther treatment. Best Regards, Reuven Mozes
  14. Hello, It seems that indeed the BinLib version cause to this issue. Please try to recover the PLC as follow: Use COM1 RS232 115200 baud rate 2sec time out Connect 6 wire cable instead of the 4 wire cable. Reboot the PLC The PLC should beep > tap once to stop the beeping Go to VisiLogic>communication & O/S, the 4th tab is system modes Check the communication by clicking on the GET button If you have a communication>Switch to Factory BOOT Go to O/S tab>check Download only the BinLib by clicking on the Advance button>BinLib (only) If the download will success, then r
  15. Hi, The link is now fixed: http://www.unitronics.com/data/uploads/software%20utilities/Unitronics_Library.zip
  16. Hello, Please provide us the following details: Did the error occur on other PC or with other PLC or MJ20-PRG? Which USB2Serial brand you have? Can you tell us what is the P/N of your Unitronics adapter and are you using 4 or 6 wire cable? If you have any doubts about the hardware functionality, contact your local distributor for replacing the PLC and the programming kit.
  17. 356 downloads

    Scrolling Text on JAZZ
  18. Dear Sir, Make sure that the PLC's COM 1 is set as RS232 1. Turn off the PLC and use it as standalone ( Disconnect expansion ,Ethernet….) 2. Touch and hold the screen 3. Power on while screen touched 4. Touch twice in Bootstrap screen 5. Update the O/S from the web in help menu and download to the PLC 6. Download a blank application to the controller
  19. Hi, Can you send the application to support@unitronics.com ? try to use an updated driver to your USB2Serial, you can download it from here: http://ftp.unitronics.com/Downloads/Drivel%20for%20SUNIX_Fixed.zip Cheers
  20. Hello, Please use the latest VisiLogic V9.0.1 (Download) and then let me know if it helps. Cheers,
  21. Dear Jay, Such PLC reaction may occurs as a results of incompatibility system files versions in VisiLogic or communication interruption. Please use the latest VisiLogic V9.0.1 (Download) and try as follow: 1. Turn off the PLC and use it as standalone ( Disconnect expansion ,Ethernet….) 2. Touch and hold the screen 3. Power on while screen touched 4. Touch twice in Bootstrap screen 5. Update the O/S from the web in help menu and download to the PLC by using 115200 baud rate and 2sec time out 6. Download empty application to the controller I hope it helps!
  22. Hello, We just checked DataXport with Excel 2010 and it's working fine without the mentioned error. Did the error message appears immediately after openning DataXport? Or, after some action? (Call,Export...) This error may occur because the ActiveX or COM DLL being accessed is not registered on the system. Please try as follow: Install the latest Microsoft .NET Framework Reboot and delete and files in the TEMP folder on your PC. These are usually located in C:\Windows\Temp and in the %temp% environment variable. Reinstall the component package that includes the DLL being accessed.
  23. Hi, The one thing that left is to try with other V130-33-R34 or another PLC. Use the latest VisiLogic version and the latesr o/s files. If you still have this problem i suggest that you ask your distributor for a working set.
  24. Hello, You can try to replace both EX-A1 & expansion cable, if you still have problem, try to replace the PLC (maybe it's related to faulty port). Also, try to download a blank application while the hardware configuration is set according to your models. For example: Reuven
×
×