  1. Hi all,

    Thank you for the answers. I must connect to PLC 8 valves, one 24V power supply and three flow meters. Every of them have RS-485 modbus communication ports. I wanted connect valves in one line but owner of this instalation don't want that solution. Now I have two solutions: 

    1. I will use  MOXA NPort 5650-16 or NPort 5630-16 with 16 RS485 to Ethernet convertor
    2. I will try to find modbus RTU to modbus TCP converter and connect all devices to ethernet switch.

    I will ask owner with of those solution he wants

    Kriss

  2. Hi all,

    I have a question... Hom many RS-232 / RS-485 modules I can install in Unistream PLC. I must connect 12 modbus lines to PLC but in Hardware configuration menu in Unilogic I can install only 4 UA-02RSC-3 modules and I have only 9 RS-485 ports - 1 in CPU and 8 on modules).  How I can solve this? Investor wants poin-to-point connecton with every single sensor. 

     

  3. I checked the PLC controller carefully and noticed that the front plastic panel is peeled off the housing. Maybe this causes some reflections in the touch panel and the controller thinks that some part of the screen is still pressed. I am sending the PLC to the seller (warranty).

  4. Hi all,
    It is possible to change screen on web server from ladder? I tried do it by action function but I can choose there only HMI screen. I need it to inform remote user about alarms.  
    User often have web page minimilized on windows try and he want to be inform about alarms by web page icon blinking,  maximalize web page  or some alarm sound on his computer. How I can solve this issue?

  5. Hello,
    I probably have a problem with the USP-104-B10 touch panel. I bought a new CPU and touch  panel , installed the control program and the touch panel behaves very strangely. At the touch of a button, the panel does not react to the next screen. It starts to react sometimes when I touch the screen in four corners at the same time. Sometimes it reacts only after about 1 minute. Modbus communication ceases to operate periodically. The web server works properly, without delays. Variables on the touch panel screen are also displayed without delays.
    the same control program on the old panel worked properly (it was created on UNILOGIC software 1.19.83), a the same  control program converted to version 1.26.90). Now I have a big problem with it.

  6. Hi all,

    I have new idea... is it possible add funcionality for moving graphical elements on the HMI and WebSerwer screens in relation with tag (tags) value (change X or / and  Y possition of the element). for example if I need to show  cage position in shaft on HMI screen and  I must place about 15 the same pictures and set visibility for them in relation of shaft position value.

    Thanks for Your involvement in improvement Unistream software. 

  7. It is possible to add possibility for grouping elements on HMI and Web serwer screens and change common atributes? for example if I want create pop-up for insert and validate values,  now I must change  visibility  parameter for every single element. Also when I want move created pop Up only for change some elements what are under the pop-up I must chceck all of pop-up elements, move it, chnge elements atributes, chceck all of pop-up elements again and move. I think this funcionality will be very useful.

  8. Hi everyone,

     

    I have a question... Is any possibility to disable part of buttons for remote operator? For example I want to restrict a posibility acknowledge of alarms only for operator from HMI panel.

    PLC: UniStream, software: UniLogic 1.9 rev.19 , remote operator or any VNC client

     

    I'm waiting for answer

     

    grettings,

    Kris

     

     

×
×