  1. Thanks for your help. We ordered another one, and you were right on with the signal generator. I was using it incorrectly as I was connecting it the same as the 2 wire transducer but it was self powered. The first unit was faulty as the second unit when installed operated correctly. Thanks Allan
  2. Im having an issue with a M91-2-r2-c Analogue input raw values. I have set jumpers 3 and 4 to B and have configured software for 4-20ma. On 4ma on multimeter I get a raw value in my MI register of 9, and 20ma I get 45. I also changed M91 and software to 0-10v with the same outcome with the raw values. I have been using a signal generator to mimic these values. This is the first time I have used these 91s on Analog and are wondering if I have missed something or the unit is faulty. Thanks for any assistance.
×
×