  1. I am trying to connect a US5-B10-B1 to an Omron NJ101-9000 with Ethernet IP. The US5 is adapter with structs for O2T and T2O. I have tested it between two UNistream PLC's and it works perfect. Today the customer came to test it on an Omron and nothing communicates. The Omron is set as scanner. He claims that they have had trouble earlier with this setup and must use Vendor Specific Objects to communicate. I monitor the connection bit on my adapter, but nothing happens. Tips? Must an EDS-file be used on Omron?

    My testfile is enclosed

    Test_EthernetIP (1).ulpr

×
×