Everything posted by Isakovic

  1. Hello, Are there any rules that are considered "good practice" when stacking expansion modules, or is it only esthetics that doesn't effect functionality. To be specific I have five PT400 modules connected to EX-D16 and had to add one AI4-AO2 module on the end. This question came to my mind when I was checking current consumption that EX-D16 can supply and saw that modules that require 24V supply have "sandwiched" temperature modules that don't.
  2. When you measure Pt100 resistance it should be around 120 ohms or so. 32767 means you are out of range and you have open circuit between points where PLC measures resistance. Either your probe is faulty or it is a wiring error, which is more probable.
  3. Post more info. What hardware are you using? Do you measure voltage on the sensor output when it is activated? Can you post screenshots of the hardware configuration and part of code where you read counter values? Also schematics how you did the wiring.
  4. I never tried it but I don't see a reason why it wouldn't be possible. Are you using serial or Ethernet? Set different ports if you are using Ethernet. *Edit I tried it and it works, two PCs can communicate with the same PLC through UniOPC. I used Ethernet connection with different ports.
  5. I needed a similar filter when I had extremely unstable reading from Pt100 probes. I made it from common elements, but this looks more elegant. I wish I knew there was a Filter FB in VisiLogic.
  6. Hello, When reading timer value as numeric data type (TCL or TPL) the result is always 0, while reading it as a string returns correct value. I don't know what's the problem. It probably isn't syntax because OPC reports syntax errors, I tried all numeric data types and the result is always 0. Reading value as a string isn't that much of a problem because substrings for minutes and seconds can be extracted. But when writing the value into PLC some code gymnastics is required which takes time. So my question is can timer values be treated as numeric variables? I use "WinLog" SCADA from Sielco, example of tags that I use: Transport.TPL0 (this returns 0) Transport.TP0 (this returns correct value)
  7. Your valve takes 150s to fully open/close, in the example 1/10 of a second is used to measure valve position, so its position will be between 0 and 1500. In the PID loop 1500 will be max output (fully opened valve). PID output is compared to register that contains virtual position. If PID output is higher than virtual position you open the valve to make this two values equal. While PLC output for opening the valve is active you increment virtual position register every 100ms, while PLC output for closing is active you decrement the same register every 100 ms (SB7). So virtual position changes every time you open/close the valve. I don't know how better to explain this concept but the example is very good. It has solved problems for dead band (valve won't move for values less than 1 second) and end positions (in position 0 and 1500 PLC output for opening/clossing remains active for extra 2 minutes to be sure it's in the right position). Before I started using this method I made some logic that opened and closed valve based on the error. It used pause and active time, if temperature is much lower than setpoint - open valve for, let's say, 3 seconds every 30 seconds, if it's few degrees under open for 1s every 45 seconds, +/-0.5 degrees around setpoint don't do anything. This could be made functional but it always oscillated. Some PLC manufacturers have function block for three point valve control, maybe it could be implemented in VisiLogic in the future, just a sugestion . It makes life much simpler in these situations.
  8. There is an example for PID loop in U90 ladder called "PID with motorized valve". You should check it out. Idea is to have a register that will contain virtual "position" of the valve expressed in 1/10 of a second (you need to know time it takes for valve to fully open from closed position, this will be PID max output). You will then compare this value with the PID output, if it is smaller than PID you open the valve, if it's larger you close it. You should have a small deadband. If output for opening the valve is active you increment virtual position register every 10ms (SB7). If output for closing is active you decrement it. I used this before with Vison and Jazz controllers and it works well.
  9. Did you assign MI0 to analog input in hardware configuration? I don't see any other possible mistake in the ladder. It's probably wiring. Could you post a drawing of your wiring? 0 volts from transmitter supply should be connected to PLC input common to get a current loop.
  10. Thanks for the response. Machine operator will need to run home routine upon turning on so I won't be needing position backup.
  11. It happened again. It's locked and socket status is 20 on all three ports I use. Still responds to pings. SB 154 and 167 for Ethernet errors are 0. How would code for resolving this look like? I think of something like: If status is 20 for 5 minutes, close the socket and init again in next scan.
  12. I had a similar problem with V700 just stopping Ethernet communication. It wouldn't communicate with SCADA through UniOPC and couldn't be accessed by VisiLogic from any port. It responded to pings. Socket status was the same as with Joe's case, 23 when it locked, 20 after restart. It happened after 20 or so days of continuous work. It started working again after everything was restarted. I never had any problems with controllers that require Ethernet cards.
  13. Hi, I opened U90 help files by mistake instead of Vision help files , and found that for HSC it says "Counter value is an integer with a range of -32768 to +32767. After the counter reaches the maximum value of +32767 it will continue to count in the negative range. " I couldn't find similar statement in VisiLogic help files. Now, I plan to use Vision controler V430, and in Technical Specifications for V430-J-TR34 it says that hardware counter has resolution of 32-bit. Does that mean that I can link ML to high speed inputs and they will count to 2^31? I am using two shaft encoders if it's of any matter. I wasn't even thinking about this question, but since accidentally I looked at U90 help it's been bugging me.
  14. Thanks for assistance, It works now. If anyone else needs it, if you use ladder comm function "V700: Read Socket Status", and compare it with 23 it's the same as SB 147-150. Just out of curiosity, do I still need CARD INIT and SOCK INIT blocks for V700 to work? I can't test it easily because I use Ethernet to communicate with it from a distance.
  15. Is there any way to see which Ethernet socket is active on V700? I went with V700 because it has integrated Ethernet port, but now I can't use SB 147-150 like on other models that require expansion card.
  16. I was looking for 2D drawing. I checked that section of the site and there ain't any files for V700. A colleague extracted front view for my project from 3D CAD so I found a way around that. Thanks.
  17. Hello, Is there any place I can find CAD files for V700. I can't find them on the site.
×
×