Hello.
I would like your help connecting my 12 analog inputs to my snap in V200-18-E6B module, EX-D16A3-RO8 module and IO-AI8 module.
PLC:V1210
1st analog signal:
danfoss fc51 inverter
analog signal 4-20mA. It is self-powered, no external power supply required.
2nd analog signal:
danfoss pressure transmitter 4-20mA
it requires external power supply 24VDC
I have turned all jumpers to current mode.
V200 questions:
1) Does the v200 module require power supply to activate the analog inputs or the power supply is required only for the analog outputs?
2) 1st signal connection to AN0, +mA to AN0 and -mA to ACM, correct?
3) 2nd signal connection to AN0, +mA of the transmitter to AN0 and 0V of the external power supply to ACM, correct?
EX-D16A3-RO8 questions
1) 1st signal connection to AI0, +mA to AI0 and -mA to 0V, correct?
2) 2nd signal connection to AI0, +mA of the transmitter to 24V from the external power supply and -mA of the transmitter to AI0, correct?
IO-AI8 questions
1) 1st signal connection to AI0, +mA to AI0 and -mA to COM, correct?
2) 2nd signal connection to AI0, +mA from the transmitter to AI0 and 0V from the external power supply to COM, correct?
Thank you in advance