Low-pass filter
AlexUT replied to Flex727's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi, Low-pass filter in Ladder is more like to DSP (Digital Signal Processing), which require special hardware module, or lot of resources. Some PLCs have a Filter option in Hardware Configuration, and other PLCs can use Filter option from FB's Menu. Please look an next link from Control Engineering: Ladder logic 402: Data manipulation and filtering. Frank Lamb. http://www.controleng.com/single-article/ladder-logic-402-data-manipulation-and-filtering/e589114a10276058909584cea125cbcf.html Please remember, that conversion time for analog inputs will be number of system scans. B.R. -
Hi hotwires, There are 2 examples of time synchronization, for V570 and V700. Both are located in Examples directory": C:\Program Files (x86)\Unitronics\Unitronics VisiLogic_C\Examples\Version 900\Project examples\Communications\Ethernet Daylight Savings Time cannot be automatic updated, as it changed from time to time. You have to take care to decide, when to change DST. Rest is done by RFC-305 FB and some logic. The same is for sync intervals. You have to select applicable for your project sync intervals. If you have a specific requirements for your project, please send us project potential evaluation with detailed requirements description, and we will pass your requirements for evaluation. B.R.
-
Hi REGEX, Adapter, you use, based on FTDI chip. :Chipset: FTDI" This chip is supported by Windows, but not supported by UniStream. To connect and use Cinterion EHS6T modem with UniStream, you have to use USB-to-Serial converter, based on Prolific chip. Unitronics supply such converters - Sunix USB to RS232 adapter model UTS1009B. This cable has been tested by us and clients and it works. Please see following link: http://www.sunix.com/en/product_detail.php?cid=1&kid=4&gid=14&pid=1136 You can use similar , Prolific chip based converter.
-
Hi Nicolche, Yes, VisiLogic does not allow to use PTO in an Interrupt Routine. What are requirements for servo (do you mean stepper control by PTO?): -Is a knife movement one direction, or both directions? -Does knife, one time activated, cut and return to initial position, or it should be returned by opposite direction movement? -How long knife may stay at end position? -Can you use "High Speed Outputs (Stepper Control)" from Hardware Communication settings? You can send all details to support@unitronics.com. B.R.
-
Hi, Such mess with an IP settings. To eliminate this, always do SOCKET INIT. Then you will have much less problems. B.R.
- 16 replies
-
Hi MattP_Mac, 1.Make ping from your PC to PLC IP. Does PLC answers? 2.Open DOS prompt at your PC and enter "telnet 192.168.1.10 20256". DOS display will blink, clean and stay black. Is this what you see? 3.Enter PLC info mode and check Socket 1 status. Is it connected? Share test results. B.R.
- 16 replies
-
- 1
-
Connecting to Scada OPC server
AlexUT replied to Paul J's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi Paul J, IP address you use is from private address space. It is not accessible direct from the Internet. It can be accessible only from the same network. If this IP address after router, you have to make port forwarding at router to access this PLC from Internet. B.R. -
Connecting to Scada OPC server
AlexUT replied to Paul J's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi Paul J, Tell me your PLC IP address (send it to support@unitronics.com) and I will check connection by Modbus application. -
Connecting to Scada OPC server
AlexUT replied to Paul J's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi Paul J, Use next example for MODBUS TCP Slave: C:\Program Files (x86)\Unitronics\Unitronics VisiLogic_C\Examples\Version 900\Project examples\Communications\Ethernet\Ethernet MODBUS IP\V280_Ethernet_TCP_MODBUS_IP_Slave.vlp This example include all required functions. -
V280 Factory Reset Issue
AlexUT replied to EXCAVATOR's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi, Please send email with PLC SN, used VisiLogic version, and problem description/display snapshot to support@unitronics.com B.R. -
how to convert u90 to visilogic?
AlexUT replied to oferyosef's topic in Jazz, M91 PLCs and U90Ladder
Hi oferyosef, Projects, developed in U90Ladder, are very different from projects, developed in VisiLogic. You have to do manual conversion for your project. -
PTO and continuously run
AlexUT replied to darknesspic's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi, PTO is not intended to manage endless movement. If you have to work without target, use PWM. In this case you have to program acceleration and deceleration in Ladder. You do not need PTO for this. B.R. -
V350 sms configuration issue
AlexUT replied to vamalgise's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi Vamalgise, I recommend to make simulation at your office. Use the same provider's SIM card, and the same modem model. Then you can trace online hot SMS was sent, and what are statuses. There is a "Send Fail Bitmap". explained in "Help->SMS Operands". In office it will be simplest to find where the error is. -
Hi Declan, How exactly do you clone?
-
V570 PID autotune issue
AlexUT replied to Vidmas30's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hello Vidmas, After 6 year some elements of PID loop will have degradation. PID FB is a piece of software, keeping all PID parameters in linked MIs and MBs, and in block of 32 MIs. Once you run PID Autotune for the first time and satisfied how it works, you have to save PID parameters for feature reference. If PID cannot work stable, in most of cases you have to check other PID loop elements. I recommend you to check all equipment in PID loop - sensor, actuator, etc. Do you use Analog, Digital, or Relay output for PID output (CV, or Control Value)? You can completely clean POD parameters by cleaning linked MIs, MBs, and block of 32 MIs. Than you have to run PID Autotune again. I hope this helps. -
Hi Rhino, Please put all blocks in chain into one net and energize from SB2. Write to SI 140 should be last in shain. Does this fix problem? *Not only '/' will switch COM port to 7, E, 1. It may be BREAK signal from weight. If you continue to have problem, send your project to support@unitronics.com for review. Unitronics have a new site - http://unitronicsplc.com Wisit it and provide us your impression. B.R.
-
EXF-RC15 and HSC
AlexUT replied to arbellah's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi, It will be due to different internal impedance. There are different V130 models with different input impedance. V130 -TRA22 have an input impedance 4.5 kohm for I 0 - I 1. V130-T38 have an input impedance 3 kohm. EXF-RC15 have an input impedance 4.5 kohm for I 0 - I 5. So it is dependent of V130 model you tested. For sensor with NPN output you have to use pull-up resistor. B.R. -
EXF-RC15 and HSC
AlexUT replied to arbellah's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
It is dependent of minimum pulse duration from sensor. As shortest is minimum pulse duration, as less should be resistor. I recommend to start from 5.1 kohm. Current will be 24/5100=4.7 mA. Check it with minimum pulse duration from sensor. -
problem math
AlexUT replied to Hamza1's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi, Google say: 1 Radian = 57.2958 Degree. Then 0.017453 Radian = 0.9999832398418258 Degree (~1 Degree). Use this in your formula. B.R. -
EXF-RC15 and HSC
AlexUT replied to arbellah's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
As I see from Quick Start Guide, outputs are PNP or NPN. So you have to use pull-up/pulll-down resistor. http://info.bannerengineering.com/cs/groups/public/documents/literature/177900.pdf Additional to this, you have to connect input terminal 10 (n/p) to either 0V or +24V - configure inputs as PNP or NPN, in accordance to used encoder. This will eliminate disturbance if one input to other. B.R. -
EXF-RC15 and HSC
AlexUT replied to arbellah's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi Arbellah, You have to connect input terminal 10 (n/p) to either 0V or +24V - configure inputs as PNP or NPN, in accordance to used encoder. Than any configuration should work. What is an encoder model? What type of output have shaft encoder you use? NPN, PNP, push-pull? In my case it works fine with push-pull encoder I have. -
Jazz remote communication options
AlexUT replied to Pawks666's topic in Jazz, M91 PLCs and U90Ladder
Hi Pawks666, Jazz use the same UART (hardware) to work with both, RS232 and RS485 interfaces. You cannot use both interfaces at the same time. -
Hi all! I found 2 critical problems with SD cards, when SD card is not detected at all, or detection take long time - more than 1 minute. 1.When SD card include non 8.3 named files. Such files will be created by some PC applications. I found one of such application is automatic disk defragmenters. Such software cteate hidden long name files on each SD/Disk on key, etc. devices, connected to PC USB port. Solution - use PC which have no such software installed, or uninstall it. Format of SD card is recommended to restore its normal condition. 2.SD card lost its capacity.Solution - download Panasonic SD card formatter from site and re-format SD card with RESTORE CAPACITY key. I restored number of SD cards by this software. 3.Do not use cheap SD cards of unknown manufacturers. I failed with such 8 GB card of unknown manufacturer in Saturn store, Germany. Bought it to have SD/Mini SD/Micro SD adapters. But SD card is not working from the box. 4.Use Safely Remove Media icon to remove SD card from PC. I hope this helps.
-
Need Help with RTD Setup
AlexUT replied to Scott59's topic in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Hi, For better help please provide more information, like RTD nominal resistance, link to RTD specification, full RTD model number (see p. 4 of document). etc. It seems, that you are talking about next RTD: http://ultra-nspi.com/product_groups/nuclear/nuclear_pdf/Models_601.pdf Current parameters you mentioned are for maximum RTD load, which in most cases is not reached. From this document follows, that there are 4 models of RTD sensors, 2x100 ohm, and 2x200 ohm. Unitronics PLCs supports 100 ohm RTD. You are not referring to PLC model. You can read V350 RA22 settings for RTD at following link: http://www.unitronics.com/Downloads/Support/Technical Library/Vision Hardware/Vision350 Installation Guides/V350-35-RA22_J_DOC13005-A3_06-13.pdf You have to configure Analog Input by jumpers, see page 4 and 6 for details, then configure it in VisiLogic Hardware Configuration as PT100 with corresponding "alpha" coefficient. Then in linked to this Analog Input MI you will have temperature in 0.1 C. having 235, you have to read it as 23.5 C. I hope this helps you to set it up. B.R.