  1. Hello,

    thank you all for quick responses. After your suggestions and contact with Unitronics support I created a final version of my program.
    image.png.ce4934176012c0f49c6b36cb45c24225.png
    Unfortunately, there are no received messages. Messages are received only during power-up of the converter (some noise). 

    I checked my cable - there is galvanic connection between pins and endings. I also swapped cables many times.

    Here is the oscillogram of the Modbus signal at drive inputs.
    image.png.8ffd7e1cdbe3a36e60f4ed5646e23da9.png

    And below oscillogram when I connect with my testing software (and it works). I know that probe's polarization is inversed. What concerns me is that the amplitude of peak-peak voltage above is 2.5V when it is 7V below.
    image.png.ac7343e6fc1226ff7083a2226c7844fd.png

    Modbus in my drive works properly as I checked it by modbus testing software on my PC (checking means sending and receiving words and operating drive remotely). BTW. Mtester - great and free software. Register which I try to read (2101 in drive, so 2100 in PLC) has value 65 - no matter as there are no received data.
    image.png.c0d2d09d2a51aef8b73da8abe196a13d.png

    MI 2 status is 4 and 5 alternately.

    Termination is done at both ends.

    Do you have any other ideas?

    Once more - when I want to set PLC Net ID with this block, numbers from 1-63 are CANopen and from 64 RS485? Does it have meaning? In my program, PLC is 1 when drive is 2. I tried also 64 and 65 with no success.
    image.png.777b8bd0ab66223f4675175ffd271a87.png

    KR, Bartosz

    1_Communication test.vlp

    image.png

  2. Hi all,
    it's my first post but I guess not least as I have a project to do using my Unitronics V1210 with CANOpen  and 2 ports for Modbus RTU on board.
    I want to establish basic communication with my VFD (Vacon 100 / now Danfoss company) by Modbus RTU.
    1. I bought RJ11 six pin plug and prepare junction so I have two cables - yellow at PIN1 and red at PIN6.
    2. I connected PLC (Port 1) to VFD (A,B inputs)
    3. I wrote a basic program to read the register 2101 (which is not 0 for sure) and... nothing happens. No communication.

    What I have checked:
    - Ports termination (set to RS485 with termination)
    -  Galvanic connection between pins and end of the cable and it is ok
    - loopback test FB - no answer
    - ID, Baud Rate, Parity, Stop Bits - they are the same in drive and PLC

    I kindly ask if someone could check my ladder diagram as I have no idea what is wrong.

    image.png.c87ec9967ec5e147d209af24da4cdc58.png

    image.png.64d74aed59a821979ee2b540e45e5db3.png

    KR,

    Bartosz

    image.jpg

×
×