  1. Good morning. I have a problemm to open program file. All time i get error message: Run-time error '-2147217908 (80040e0c)' Command text was not set for the command object. I dont know what VisiLogic version subcontractor use for build this file. Please help. Thanks Yuri
  2. Thanks for advise. I'll change it. Can you explain how i can read output bit O25 ( adress i have put in Kepware ?). Inputs reads OK. With outputs something wrong.
  3. Thanks to all for help, problem was fixed by changing Socket 2 to 502 in setting touch panel (not in a program)
  4. Thanks for reply. But i dont understand where i have change configuration? Is it not already configurated ? Or I have to open socket 2 in SOCK INIT module? And other qustions: what means in KepServer, number after IP (<172.21.204.37>0) ? And where i can find it in my PLC program? Thanks
  5. Hi to All. I have V700 project configurated for Modbus IP I try to make connection whith PLC from KepServerEX 6.6 I try to read MI5 (40006), but when I running the QC in the OPC the tag quality is" BAD" and the value is "unavailable". I am not sure, if configuration correct from both sides. Can anybody help.
×
×