Thanks for the suggestions!
So far I've double checked the hardware settings, and they appear to be correct.
I have 0-10v selected on analog input 0.
I tried wiring both sensor wires to a separate power supply. (red sensor wire connected to 24VDC + and black sensor wire connected to 24VDC-) with the white wire still connected to T+ at AI0.
After doing so, the designated MI would sporadically bounce between 0 and 22. When I unplugged the sensor from the cable while the cable was still wired, the MI would bounce between 0 and 33. I tried to change filter strength to see if that would level out, however there was no change. Not seeing any change in value with a respective change in pressure at sensor.
Ausman, just to clarify. Are you saying that its important to have (V1 V0 ) and (V2 V0) powered simultaneously? I currently only have 24VDC to (V2 V0).
Also, I measured a voltage of about 0.4 VDC between white and black at roughly 25 psi (the most pressure I have available at the moment). If I did my math correctly, the power output seems to match the voltage scaling on the sensor. This is a 0-500 psi sensor, which should be about 0.02 V per PSI. that should place it at 0.5 V at 25 psi. This was done while the sensor was connected directly to the power supply.
Thanks again!