  1. I have tested the download today and it worked with out a problem. I extended the time out time to 4 sec, increased retry’s to 12, ensured no remote access from mobile and and changed the sb168. The plc now has a copy of the software burnt in flash. Thank you for you help with this it is really appreciated.
  2. SM-J-RA22 controller When I connection via remote app in iPhone I get a red screen when trying to change a variable. My iPad and another persons phone does not do this. I have checked all devices have latest version of remote app. I have attached the screen shots of each. On the red screen the number pad does work if you can Rembrandt the location of the keys.
  3. Thanks for the suggestions, I will review power supply. I don’t have a spare unit. I will be testing this download again today.
  4. Hi Ausman thank you for your feedback, I haven’t programmed many plcs and this is my first Unitronics. I do appreciate your advise and do not consider it rude. I have the power up value for SB168 =1 and it removed the error. I am guessing this then allows the plc to change the value when it needs too rather than it being held at 1. I use MB51 to control the trends which I want to run continually, can I just set it to 1 on power up or is it best to just do what I have done in the attached. I will be testing the download all&burn today. I have also noticed that if someone access the HMI via there mobile app it will interrupt the download. cheers Dermie
  5. Hi kramtel i have checked the memory and I have used about 1/4 of the space. I have attached a screen shot. Is there any specific areas that I should be checking in case that specific section is over it’s allocation. I have extended the time out and number of retry’s and will test again today. thank you again for your help.
  6. Hi Ausman i have set SB168 to 1 but it still gives me this error, why would it do this? I have now set the timeout length to 4 seconds and the number of retries to 12 and will see how it goes today. thank you again for your assistance.
  7. Hi I have an SM-J-RA22 controller with ethernet adaptor and having failure to “download all& burn”. I have always been able to down load via serial or ethernet connection but today when I tried to do a “ download all&burn “ it gets half way through the down load it it looses communications . I have tried this on ethernet connection and then tried again with a serial connection and got the same result. Each time the de play would stay on the Unitronics logo and I have to drop power to the PLC and restart it to get the HMI working again. It did allow me to do basic down load successfully. I would appreciate any advise someone can supply on what the problem may be.
  8. Yes , the current day was 7 but when I reset the RTC it changes to 1 for a Sunday. When I download a updated program the day is always 1 day behind and with in 2 hrs of the download it corrects its self or if I select “set RTC” . This morning I did an initialise & Reset, then downloaded a blank program and then reloaded my program and the day of week was correct . I will monitor this over the next week to see if the problem occurs again. I really appreciate the time you give to assist me with my programming issues.
  9. Attached is a screen shot that shows my visilogic version 9.8.91 build 0. I don’t want to do an inialize and reset of the plc until I am in the factory next to the plc tomorrow morning. I am in Australia and it is 20:25 Sunday night. If I get the rtc current values on the comms page it shows the days is wrong. when I set the rtc from the comma page it corrects the day straight away. I have just downloaded the program again and then checked the comms page by getting rtc current values and they are correct. .When I “set RTC “ may have corrected the issue, I will monitor this over the next few days to see if I see this issue again thank you for your help on this.
  10. Thankyou for that. I did post on what I thought was a related topic but could not find it again.
  11. When I download a new copy of the plc program the RTC shows the day wrong. Example attached the date is 23 Jan 22 and the day is shown as Saturday. This corrects it self after a few hours of the download. Also attached is the region number of software. I have seen this issue on the forum but it advises the issue was corrected a few years back. Any hits on how to address this would be appreciated.
  12. I can not change a variable on the hmi. I have MI 61 setup on one page and it allows me to change the value from the HMI. I have what looks the same setup on another page and it will not let me change the variable. They look to be setup on each page but one page will not let me change the setpoint.the one with the increment of 11 does not work. any help would be appreciated. cheers wayne
  13. Thank you for the reply Flex727. The install manual states to set jumper 11 to set to B if you are using a pt100 in AI 1 or 2 to create the CM point. The documentation implies I can have AI#0 as a PT100 and AI#1 as a thermocouple type K. The thermocouple input is not working properly and I wanted to confirm that I could mix the type of sensor I use on these inputs.
  14. Thank you, it was the jp11 not set correctly. If jp11 is set to B can one of the analogue inputs #1 be used as a thermocouple input or do they both need to be pt100. I have a thermocouple on input #1 and it reads correctly sometimes then it gives strange numbers for a while.
×
×