Everything posted by Gabriel Franco

  1. Why 9600, 8, n, 2? It isn´t usual. I suggest you to double check COMM INIT and Modbus Config blocks to match VFD parameters (baudrate, data and stop bits, address).
  2. Or simply use three different tags, one for each period, updating (SUM) them in each scan or in a base time. This way, you have instant values for all your periods. Of course, you will need to reset those tags at the right time (daily, weekly, monthly).
  3. Use LINEARIZATION FB. Keep in mind module resolution is 0.1°C, that´s the reason X1 and X2 values are -2000 ... 6000 in the image
  4. Take a look to the module specs. It shows register values when analog input is out of range. https://myzone-kza3sadj.netdna-ssl.com/wp-content/uploads/2015/12/IO-ATC8.pdf
  5. I perform manual tuning when I have temperature process instead of auto tuning. I have better performance. In general, to reduce overshoot, decrease P, but all systems have their own behavior.
  6. I guess you´re using Remote Access software to show your Vision 130 and you believe it is a simulator. However keep in mind that all Unitronics software requires a physical PLC in order to view online data. There is not simulator.
  7. It would be nice to have an option to save VLP file including registers values
  8. I always use terminal resistors at both ends of an RS485 network, even in point-to-point short cables. Also, I use shielded cables ground at a single point. Rarely had problems with this.
  9. For settings, if those are saved as registers, you may use "Export PLC Operands to Text File" under Connection menu. I use to save operands file together with VLP and OS files as a full backup of my applications.
  10. Calibration data keeps on IO-LCx module.
  11. You are using direct contacts instead of coils for VALVE SET / VALVE RESET
  12. I suggest you to manually tune your PID system using any of well known methods, e.g. Ziegler-Nichols
  13. I suggest you to SET HMI_START_N2 using your button, and RESET it in logic, just after INC SYSTEM_STAGE_.... Then, do not need positive transition of HMI_START_N2
  14. It would be great to have a serial comm monitor in Unistream like in Vision. This tool is the first I use to check comms problems and let me check at HEX level.
  15. In Samba ther is not a direct way to link data tables to HMI. You must build from scratch and use pointers to show files and if your data table is too long, you must show pages individually.
  16. I see no problem with csv files other than spaces added. You are using MI62 twice in fields to add file. Why?. For debuging purposes, I suggest manually enable rung 41, instead of SB13. Keep in mind that, SD operations may take a while and trying to add a new record every second may not be possible. You may try also numeric field for all those numeric values, instead of indirect text.
  17. I suggest to check CSV file using a text editor. It could be a separator and regional settings issue
  18. I´ve used mass flowmeters with Unitronics and other PLC brands. Usually I use analog 4...20 mA to measure flowrate and pulses to count/totalize or communications whenever is possible. Some of them have active outputs and others passive like any other instrument.
  19. To discard any hardware issue, I would check behaviour of any (or all) operand value after restarting power considering that, operand values are also battery supported.
  20. I had similar problem once. After a week strugling with it, I decided to install a new Ethernet card and problem was gone. It may be a hardware failure .
  21. Usually I use same Refresh bit for all Text fields and then SET it in ladder once per second.
×
×